Repair of chloride attacked concrete
Does anyone know a procedure that describes how to repair columns (60 cm of diameter) with high chloride content that caused rebar corrosion.
The chloride content is higher than the maximum allowed by the code up to more than 10 cm deep in the column.
Thank you.
RE: Repair of chloride attacked concrete
Once you have assessed the overall damage, it's a matter of cleaning the damaged concrete, protecting the reinforcing and patching. You have to be careful that the repair does not force the corrosion to the outside of the patch (corona effect).
Dik
Is this the same project where we keep telling you to replace the columns?
I've used Vector on many projects and they are pretty good.
Dik
Thank you,
Yes Jayrod, it's the same.
Is chloride extraction useful after the rebar corrosion has reached an advanced stage ?
Is it cheaper than reaplacing a column of 12 m high ?
No. And no.
concur
Dik
I appreciate the fact that you are exploring all options for remediation. However the owner needs to realize that the cheapest and fastest way to repair the problem is to replace the columns.
Jay... didn't realise it was an earlier posting.
Dik
Thanks, Dik