Thermistor vs RTD for VFD driven motor
Thermistor vs RTD for VFD driven motor
(OP)
Why Thermistor are preferred by users over RTD for VFD driven motor winding temperature measurement.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Thermistor vs RTD for VFD driven motor
|
Thermistor vs RTD for VFD driven motorThermistor vs RTD for VFD driven motor(OP)
Why Thermistor are preferred by users over RTD for VFD driven motor winding temperature measurement.
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesThe world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
Engineering-centric businesses face a number of challenges today, but unmanageable design and change processes don’t need to be counted among them. Download Now
|
RE: Thermistor vs RTD for VFD driven motor
RE: Thermistor vs RTD for VFD driven motor
A.
RE: Thermistor vs RTD for VFD driven motor
Generally, a motor will not be equipped with RTDs unless the NP HP > 250hp.
I would have to assume that installed-cost is why thermistors are preferred over RTDs.
GG
ps ControlsDude: A Thermistor is an analog device, and not a discrete device. The discrete device, often used for motor over-temperature protection, is often called a Klixon.
"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)
RE: Thermistor vs RTD for VFD driven motor
When an electrician next time refers it as a thermistor, I will tell them that name. I am sure they will just cuss under their breath at me.
RE: Thermistor vs RTD for VFD driven motor
A Thermistor is a "Thermal Resistor and looks like any other resistor, but it is different in that it has a somewhat sharp "knee point" in which as temperature changes, the resistance changes rapidly. you can have thermistors with a Positive Temperature Coefficient of resistance (PTC), in which the resistant RISES as temperature RISES, or a Negative temperature Coefficient of resistance (NTC), in which resistance DROPS as temperature RISES. Generally motor protection thermistors are PTC, meaning as the motor heats up to a threshold point, the resistance rapidly changes from low to high, creating a voltage drop on a circuit going through it. So it is very easy to make a circuit to monitor that voltage drop. If you then have that circuit in something, like lets say a VFD or an OL relay, then if you want to use that input for something else, opening a dry contact has basically the same effect, so your input can easily serve dual purposes.
An RTD (Resistance Temperature Detector) is an ANALOG device, meaning the resistance changes in a somewhat linear fashion with temperature, so you can use that to track temperature CHANGES over time. That can be a lot more useful in an intelligent protection system to avoid shutdowns, compared to a thermistor that is going to act more like the "idiot light" telling you your car engine over heated, which by the time it comes on means it's already too late. The problem with using an RTD is that it then requires an ANALOG input into something with enough intelligence to not only track the values, but be able to adjust for any non-linear aspects of it, however minor. So RTDs require more of an investment in the device that will monitor them.
Some high performance VFDs have options to add analog input cards calibrated to accept RTDs, but many even low end VFDs will offer a Thermistor Input, either separately, or one of the basic Digital Inputs will be capable of accepting a thermistor. that's because in areas of the world outside of North America, using an Explosion Proof motor on a VFD REQUIRES the VFD to accept a thermistor input.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: Thermistor vs RTD for VFD driven motor
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Thermistor vs RTD for VFD driven motor
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: Thermistor vs RTD for VFD driven motor