what is the proper isolation joint to use in this situation

what is the proper isolation joint to use in this situation

what is the proper isolation joint to use in this situation

(OP)
I saw a drawing before where it used tar paper to separate existing footing to new footing.
While I can use isolation joint at the side of the pile, not sure what to use on the top of pile to separate it from bottom of slab.
Any suggestion?


RE: what is the proper isolation joint to use in this situation

Why isolate the top? Can use cut 'sonotube ring' or better, polyurethane wrap, to provide a gap for installation, and remove it the first time it is lifted. Careful though with sonotube you may have difficulty removing the concrete. One of my first slab on grades (when I was a real know-it-all rookie) I had plywood separation strips, and I was positive the concrete would shrink away and it would be easy to pull out the plywood strips... betcha they are still there...

Dik

RE: what is the proper isolation joint to use in this situation

(OP)
That's why I'm asking because I don't really know what to use. I've not used isolation joint for this purpose before (needing to lift the slab).

I only want the slab (2nd pour) not to bond with the drilled pier for easy lifting.

RE: what is the proper isolation joint to use in this situation

Use asphalt felt (No. 30 felt) or coat the top of pier with asphalt mastic. Both would actually be better. Be sure to coat down the side of the pier past the expected depth of concrete cap. Don't rely on synthetic liquid bond breaker.

I doubt actual "tar" paper is readily available.

RE: what is the proper isolation joint to use in this situation

Cast the slab separately from the piles, then set it on the piles

RE: what is the proper isolation joint to use in this situation

(OP)
Thanks Ron

Motorcity - I was thinking about that but I want the slab to have some more lateral resistance instead of just relying on friction.
The possibility of this slab being lifting after in place is small.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources