Megging a motor through MCC has any restriction?

Megging a motor through MCC has any restriction?

(OP)
Usually maintenance execute IR test and megging directly from motor cable box, but as an effort to save time testing it and also to cover the entire system (motor+cables) my fellow engineers are sugesting changing this procedure, making this tests throught MCC terminals.

Does it have any restriction? The test results are going to be as accurate as direct in motor cable box?

RE: Megging a motor through MCC has any restriction?

As long as you isolate the connections path so it does not back feed to some electronic component inside the mcc such as a VFD, softstart, or solid stat overload. If you did not I think you would damage these type of electronics.

RE: Megging a motor through MCC has any restriction?

My utility uses this approach in medium-voltage metalclad switchgear by means of a ground-and-test device racked into the cubicle in place of the circuit breaker; provided the precautions controlsdude listed are undertaken, shouldn't be an issue, in my view.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Megging a motor through MCC has any restriction?

It's a cheap and quick and dirty test.
That said, it has value.
If your reading is good, then the motor, any part of the starter still in the circuit and the feeders are all good.
If the reading is bad, then you have to test further to determine whether the failing resistance is in the motor or external to the motor.
This test has the advantage that tests may be completed so quickly and conveniently that it lends itself to much more frequent testing than a test of the motor only with the motor disconnected.
I would support this testing method.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Megging a motor through MCC has any restriction?

That is how we test all of our installations. Then if there is an issue, you can work back to the motor as waross said. If you have been trending, a new procedure would change your comparison data. I wouldn't expect much difference but there will be some from testing directly at the motor. If your just passing or failing, then there will be no difference.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources

eBook: Metal 3D Printing
Metal can provide strength like no other material can and, throughout our history on Earth, humans have learned to harness metals for ever greater specialized applications, from radiation shielding on spacecraft to conductive components on circuits. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close