Canadian code for existing buildings
2

Canadian code for existing buildings

Canadian code for existing buildings

(OP)
Is there something in the Canadian code comparable to 5% allowance/check in IEBC section 706 ?

RE: Canadian code for existing buildings

Yeah, we have NBCC commentary chapter L. It's reliability based and pretty useful in many instances. Building been standing a while? Use lighter loads.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Canadian code for existing buildings

The NBCC is pretty limited as KootK noted... if you are in Ontario, there's Part 11 that accommodates older structures.

Dik

RE: Canadian code for existing buildings

(OP)
exactly what I needed. Thanks Kootk and dik a job in ON and BC.

RE: Canadian code for existing buildings

The problem with NBCC is that it's largely discretionary on the part of the OHJ AHJ, whereas, Ontario the application of Part 11 is a much better approach. Not looking for a fight, the OMB in Ontario is quite friendly to the application of Part 11 in the event an OHJ AHJ objects... but, time consuming.

Dik

RE: Canadian code for existing buildings

(OP)
Thanks dik, we'll study it. may be asking another question shortly.

RE: Canadian code for existing buildings

dik,
One issue I have been having with Part 11 of the Ontario Building Code is this:
- Remedial action is needed if the Performance Level (PL)of an existing building is reduced due to construction work.
- PL is reduced, per the code, if the Major Occupancy is changed, Live Load is increase, or the occupancy load is increased by 15% or more. What happens if a shear wall is removed, for example? It is clear that the PL is increase in this case but the code doesn't mention anything about lateral loads, unless part 11 is considering wind and seismic loads Live Loads, which is inconsistent with other parts of the code.

RE: Canadian code for existing buildings

It's a matter of reviewing this with the AHJ, explaining, that the proposed alternative is an improvement in what was existing. This improvement, or at least, no loss in function, is the crux of Part 11.

Dik

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources