I work in a large research lab with many individual lab spaces. For the last 50 years, we have used GE DH bus duct rated at 3 phase, 208 volt, 100 amps. That product is no longer available and parts are getting harder to find, so I was wondering what others might be doing for bringing similar power capacity into their labs.

RE: Research Lab Power Distribution

Gee, search the web on bus duct and you will find more than a few sources.

RE: Research Lab Power Distribution

(OP)
Actually, Starline is the only manufacturer that makes anything similar in a 100 amp size. No one else does that I can find online. The problem with Starline is the attachment is similar to track lighting where you insert and twist to lock-in. I'm not that comfortable with that arrangement, so hence why I was wondering if I may have missed some other product online. GE makes Spectra bus, but it only comes in 225 amp size and bus plugs are way too large.

RE: Research Lab Power Distribution

Oh, I did not catch that you said 100A. Wow, that seems small for bus duct from my work history. Eaton, MP Husky, Square D, GE .... each have a line, but I think they stop at about 600A. I looked up Starline, and it has me intrigued, I might need to read up on that concept. It seems people have moved to circuit breaker panels with individual lines to the loads. I might consider the small bus duct concept on my next job. I learned something from this.

RE: Research Lab Power Distribution

"The problem with Starline is the attachment is similar to track lighting where you insert and twist to lock-in."
Assemble issue mentioned above
Starline twist and lock is assembly and anytime you do this procedure is to turn off power. Then do the twist and lock. Turn power back on.

RE: Research Lab Power Distribution

We have hundreds of feet of 3-phase 208/120V Starline in the shop where I work, and it's very reliable. It is similar in concept to track lighting connections, but MUCH more robust. It's designed for industrial use. Correct procedure is indeed to power down the run before adding or removing a tap box (which normally contains the necessary OCPD for the cord drop in the form of a DIN rail -mount QO breaker and enclosure). However, many people rather foolishly leave the power on when moving taps - really dumb.

I wouldn't worry too much about the Starline. It works well, and we've rarely experienced issues. The only real issue is when the forklift drivers don't pay attention, and snag the cable drops.


SceneryDriver

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close