Can anyone help me with the equation for profiling PT cables in Reverse Parabolic shape?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Post-Tension Cable Profiling
|
RE: Post-Tension Cable Profiling
http://www.adaptsoft.com/resources/Aalami_CI_Mar03...
BA
RE: Post-Tension Cable Profiling
If adjacent spans are significantly different (with differing inflection points) sometimes a compound parabola is used.
Things to keep in mind: check with the PT supplier/manufacturer on the systems MINIMUM tendon radius/curvature, and adjust your inflection points to maintain such a minimum. The manufacturer will also have a minimum straight-length distance that is applicable behind the anchorages.
Is this an unbonded PT slab tendon system or a grouted multi-strand beam tendon? The latter typically require a bit more 'finessing', especially if it is a bridge structure.
RE: Post-Tension Cable Profiling
RE: Post-Tension Cable Profiling
There is no single equation to do it properly using defined radius of curvature for the curve. We do have a solution in our software but unfortunately I cannot give that to you as everyone else has paid for it!