Interesting fault video

Interesting fault video

(OP)
As seen on Facebook, I downloaded the video (attached) for a tree hitting an OHTL.

I wonder how the protection didn't act quickly enough to avoid that much arcing? A flashover (not involving earth) seemed to appear pretty much as an Over Current to the substation that the relay didn't act on?

I don't know the line voltage here but looks like something around 115 kV or less, the tree/wooden pole isn't a good ground connection (Ground fault not working), it doesn't seem to be an auto-reclosure neither(isn't it?)..... phase-to-phase arcing is what I guess here..



RE: Interesting fault video

Google "Jacobs Ladder" and/or "Travelling Arc".
It doesn't take much to move an arc along parallel conductors.
I can't explain the final arc to the right.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Interesting fault video

The wires to the right are bouncing around all over the place before the arcs to the right. It occasionally happens that a fault downstream will cause phase conductors upstream to bounce around enough to cause additional faults.

RE: Interesting fault video

(OP)
Yup, it is Jacobs ladder, but why overcurrent protection didn't act? poor relay setting?

bouncing due to short circuit forces is common.

RE: Interesting fault video

Maybe, the arc is too long to pick up anything. An arcs voltage drop is 440v a foot so maybe it would be hard to pick up phase to phase?


There is one just like this but up on transmission in Dallas in 2010-2011. It went on for minutes before it was cleared. It is on youtube someplace, I know.

RE: Interesting fault video

Arcs can have considerable impedance compared to a bolted fault. As a result over current and step distance may not pick it up, or not pick it up fast enough, especially when said over current is set close to the conductor's damage curve. Line length can also play a role. A fault at the end of a very long line can look like an mild over load to protection relays. In fact very long distribution lines often have a recloser added 2/3 or more down the line to catch faults at the far end because the substation relays may not catch it (just looks like heavy load). About the only element which cuts out under nearly all fault conditions is differential protection, but outside of 230kv and above or exceptionally short 115kv lines its often impractical.

RE: Interesting fault video

(OP)
how a differential relay will pick that? current summation is still zero on these two phases.

I think a phase-balance will pick that, but looks like the line isn't protected with this function, not common to see it though.

RE: Interesting fault video

Differential applied to each phase would certainly see it, but a residually-connected differential wouldn't.

RE: Interesting fault video

It's the big, lower impedance, all three phases arc at the end that finally gets the breaker's attention.

Keith Cress
kcress - http://www.flaminsystems.com

RE: Interesting fault video

Current summation will not be zero on those two phases as current entering the line will not be the same as current leaving the line. Assuming there are no tap loads one could easily set the differential to be sensitive enough to pickup up on it and trip.

RE: Interesting fault video

@Piterpol: Very true, but in some cases there still can be limitations in regard to secondary faults on a delta-wye transformer feeding a distribution system.

RE: Interesting fault video

Numeric time overcurrent relays with instantaneous reset. Each fault lasted less time that required to time out and every time it extinguished and started over again there was at least 0.25 cycles during which there was no fault current.

RE: Interesting fault video

Mbrooke,

I knew the protection engineer that was with the utility this happened on. There is a rural co-op that covers over 3/4 of Oklahoma. They only had one protection engineer. When he retired, his job got outsourced to a relay manufacture. The utility has been looking for a protection engineer for years and they are actually offering pretty decent pay ,extremely decent if you take into account the cost of living, but nobody wants to move to Oklahoma. If someone took the job, I think they could raise a family and save 2 out 3 or 3 out of 4 paychecks.

RE: Interesting fault video

Did he say what the problem was? Or was this an outsourced relay?

RE: Interesting fault video

I was with that utility when it happened but never heard him talk about it at the time. I was in another department.

RE: Interesting fault video

If you know his number ask, Id be really curious.


In regards to the job opening, is it something that someone can do from Home?

RE: Interesting fault video

Mbrooke,

Don't know his number or remember his name. I don't know how technical of a response you would have gotten. The guy worked his way up from a technician to being the relay guy. He retired at like 50 because he had kidney problems and had the money since he never had kids.

Maybe, I don't know. I think most utilities would like a guy on site for resolving outages. Maybe, they just need a guy for project work. I don't know.

RE: Interesting fault video

Hard to say, but maybe 69kV. Saw 2 ph-faults, with no obvious trip on the first ph-ph event, sort of implying impdance relaying was not in use. Assume 600A line, from size of conductors, indicating a 1000A pickup. One phase at 69kV = 40kV phase to ground. Just to pick up the overcurrent relay implies on the order of 40MVA. Those signle phase arcs were a tad short of 40MVA.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close