Cascade controller set-point units
When a controller accepts a remote set-point in cascade mode from another (primary) controller does the output of the primary controller have to be scaled into the engineering units of the secondary measured value (MV)?
RE: Cascade controller set-point units
Yes.
xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.
As Xnuke says: Yes.
But, I've worked on some DCS Systems that don't allow changing the Output Engineering Units of the Primary Controller - they were always 0 - 100% and could not be changed to match the engineering units of the secondary controller (like degC). It's very frustrating.....
______________________________________________________________________________
This is normally the space where people post something insightful.
input the controller output signal into a math block, scale it, use the math block output
Thanks controlnovice. On the DCS systems that don't support changing of engineering units is it just assumed that 0 to 100% output of the primary controller represents 0 to 100% of the the secondary controller measured variable? I.e. if the secondary controller measured variable is 0 to 50 litres/min then the remote setpoint is also a 0 to 50 litres/min signal?
Yes:
0-100% of the Master controller output represents the full range of the Secondary controller PV...in your example 0 - 50 lpm.
Keep in mind that typically the Setpoint range of the secondary controller matches the PV Range...so your SP Range would also be 0 - 50 lpm.
If you limit your setpoint maximum to, for example 40 lpm, the 100% output still represents the 50 lpm but the secondary controller won't go above 40.
Thank you this was really helpful.