Unexplained momentary power outages
I was recently asked to look into momentary power outages at a facility that has been experiencing re-occurring momentary outages that is causing motors to drop out and electronics to reset.
This facility is served at 4.16kV from the local utility through a M-T-M 4.16k Switchgear lineup. We recently connected a meter to the secondary metering equipment (Pt's and CT's) at the 4.16kV Switchgear main in order to try to capture one of these momentary outages. (Other main is open with Tie Breaker Closed. During these outages no relays pickup nor do any breakers trip.
We were able to successfully capture one of these momentary outages and found that the voltage drops all the way to 0V for a duration of approximately 600ms before it is restored back to 4.16kV. Approximately another 566ms later the voltage drops close to 0V again this time for a shorter duration of only 92ms. This was the only event we were able to capture during the monitoring period.
I've included an attachment that shows the voltage and current trends during this event. The first two trends show the voltage and current respectively and the third trend shows the voltage and current of one phase on the same trend. Looking at these trends it appears that immediately after the voltage starts to decay the load current quickly increases. This is likely to be expected with motor loads which it mostly what this facility consists of (chiller loads etc..)
Any ideas on what may be causing these momentary outages. It would appear that it has to be something happening on the utility end? Could this perhaps be a re-closer or some other automatic protective device on the utility side opening and then re-closing quickly?
RE: Unexplained momentary power outages
Is this facility near the coast?
In my instance I talked to an engineer at the local utility.
He explained that they had some feeders running parallel to the beach.
During the dry season, winds would blow spry on to the insulators.
The moisture would evaporate and leave a film of salt on the insulator.
Getting into the autumn as the humidity increased and light rain started, the salt film would become conductive and flash over.
That would cause a serious voltage dip across the entire city.
As the rain became more intense the salt would be washed off the insulators and we would be good until the following autumn.
If you have a contact with the local utility he may be able to give an explanation.
Bill
"Why not the best?"
Jimmy Carter
CR
Can you explain the tap fuse blowing the clear the fault and the associated quicker time delay? Would this be the tap fuse on the overhead distribution line?
So if I understand correctly there appears to be a fault somewhere between substation and facility and when fault occurs the re-closer opens/closes first and when that doesn't clear the fault the tap fuse blows? I'm assuming this tap fuse is on another line/tap that is not serving the facility since it does not take the facility out permanently? What would cause the dip while the tap fuse is blowing?
Waross
This facility is fairly near the coast (aprox 10-15miles from beach). We have been experiencing a lot of seasonal rain lately so perhaps there may be a correlation between the rain and these dips/outages.
But the fault wasn't gone, so instantaneous is now blocked and the relay time overcurrent starts timing toward a second trip. While that's happening there's enough time for the tap fuse to blow and the event ends without a second breaker trip.
The fault pulls down the voltage at the fault location and that impacts the voltage everywhere on that feeder and on any other feeder sourced by the same transformer at the substation.
Your explanation now makes sense. Thank you.
The one follow-up question I had was for the time period between when the re-closer closes and the fuse blows. The voltage is restored to normal for approximately 566ms. If the fault is still there wouldn't the voltage be depressed immediately after the re-closer closes and not return to close to normal for 566ms?
Is 600ms a typical time for a high speed re-close?
600ms is in the ball park for high-speed reclose. Maybe a bit slow, but not bad. I've seen many cases where the whole fault-trip-reclose sequence takes less than 500ms.
Don't worry about the cause, as it's the utilities problem. Salt spray, animals, back hoes, dump trucks, bad drivers, etc. Look at the frequency of the events, not at what people say is all the time.