NFPA 13D live load requirements

NFPA 13D live load requirements

(OP)
I posted this under structural, and it was suggested I post it here also:

NFPA 13 has section 9.2.1.3 Building Structure, which requires a 250 lb live load requirement at the point of hanging, intended to account for a person's weight at that point. Unless I'm just missing it, I see no similar section in the NFPA 13D low-rise residential code and I'm having trouble locating anything that kicks back to the main NFPA 13 for structural design requirements.

What, if anything, requires the 250 lb live load in low-rise residential structures?

RE: NFPA 13D live load requirements

No live load provisions are prescribed for water filled fire protection piping in the 2012 International Residential Code or NFPA 13D. Given the amount of water in these systems and the materials of construction (CPVC or Cu tubing), the added weight of water filled pipe has been found to be neglible and doesn't create any safety issues based on the IRCs prescriptive construction requirements.

You're mixing your standard numbers with your building types. You stated

Quote (wikidcool)

I see no similar section in the NFPA 13D low-rise residential code

The first answer was based on the requirements in NFPA 13D for one-and two-family dwellings and townhomes constructed to the IRC. The design of an automatic sprinkler system for multi-family housing that is not classified as a high-rise building is generally governed by NFPA 13R. In the case of a NFPA 13R system, Section 6.13 requires pipe hanging and bracing systems comply with NFPA 13. Multi-family housing is subject to the requirements of the International Building Code.

RE: NFPA 13D live load requirements

(OP)
Thank you. To confirm I understand your reply correctly:

For one and two story dwellings/townhomes governed by NFPA 13D, there is no 250 pound live load requirement at the point of hanging.

But for low-rise multifamily governed by NFPA 13R, Section 6.13 requires compliance with NFPA 13 in this regard, so the 250 pound live load IS required.

Correct?

RE: NFPA 13D live load requirements

Correct. Based on NFPA 13R Section 6.13, the specified live load requirement is applicable. NFPA 13R references NFPA 13 Chapter 9 in its entirety.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close