ABB REL650-REL670 protection XRIO Problem (OMICRON)
Hi friends ,
I have a problem , I export my relay parameters as xrio , But i couldnt import Omicron File. Is it possible to import parameters to Omicron file _?
RE: ABB REL650-REL670 protection XRIO Problem (OMICRON)
If the setting criteria include a zone 1 trip at 85% of the line, it should be sufficient to know that the relay trips zone 1 at 80% of the line and trips zone 2 at 90% of the line.
If you look at just below and just above the zone 1 setting, as set, and read that out of the relay and then use those as test values you might as well stay home, you've not done anything of any lasting use.
If the relay is actually set with zone 1 at 120% of the line, the 90% trip that turns out to be zone 1 will be a clear red flag, but if you read the settings in use test values based on those all you'll do is prove that the relay trips at (say) 121% of the line and doesn't trip at 119% of the line without ever making note that the set point is ridiculously wrong.
Test sets should never, never, ever know what the actual relay settings are.
davidbeach I think you didnt get what I mean :)... I do this job for 3 years..I did this many time for Alstom Micom,SIEMENS, Schnedier Sepam,GE,SEL.....But for ABB i coulndt import,
It s not about settings, I can test relay without test set.
Thanks for your time.