locked rotor current > FLA?

locked rotor current > FLA?

(OP)
Is locked rotor current always, and I do mean always greater than full load current. I know shaded pole motors LRA is close to FLA,
is their LRA always greater than their FLA? Is there ever a motor or condition where FLA could be greater than LRA?

RE: locked rotor current > FLA?

Don't see how that could be. FLA = Full Load Amps, so how could locking the rotor not result in the motor being at LEAST fully loaded? The definition of "Load" would need to be something not related to shaft power, and why would one have a motor if that's the case?

So curious minds what to know why you are asking this question? Have you observed something along these lines?


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: locked rotor current > FLA?

(OP)
I have not observed something else, I want to be sure the term always would apply to what I am trying to write. I want to avoid a blanket statement if there are any exceptions. Thank you for your reply.

RE: locked rotor current > FLA?

The terms "Locked Rotor Current" and "Full Load Amps" and particularly "Locked Rotor Current" are mostly used in connection with squirrel cage induction motors and synchronous motors.
In the case of torque motors locked rotor amps and FLA are often equal.
A wound rotor motor may be configured as a torque motor with lots of rotor resistance. In this case, the locked rotor amps may be less than rated full load amps. Of course the motor will not produce full load power with that much rotor resistance.
Actually, without supplementary cooling, the locked rotor amps will be a lot less than rated full load amps.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: locked rotor current > FLA?

So with the locked rotor providing no power to the mechanical load, you are a long way away from the full load condition.

RE: locked rotor current > FLA?

FLA or full load amps is the current the motor operates at when operating at its nameplate power rating. SEA or safe full amps is the highest current the motor can operate at continuously. It's the FLA multiplied by the service factor. Typically 1.15-1.25 times the FLA. LRA is the maximum current the motor can possibly dra. It's typically 4-6x FLA and calculated by measuring the resistance of the windings and voltage applied. It's the inrush current during a direct on line motor start.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close