480 - 240V Transformer check.

480 - 240V Transformer check.

(OP)
I have 480V 3ph (about 40kVA) and need to hook up a 230V machine. We're looking for a transformer and I believe we want a Delta-Delta and not a Delta - Wye. The machine has no neutral connection.

Seems we can find lots of Delta - Wye here about. I should probably hold out for a delta secondary right?


Keith Cress
kcress - http://www.flaminsystems.com

RE: 480 - 240V Transformer check.

No, go for the delta-wye. Ground the neutral at the transformer and just take the three phase conductors to the machine. That way you have a properly grounded system.

RE: 480 - 240V Transformer check.

Hey David, maybe it's too obvious, or just me, or that you haven't said so, but would it not also be advisable to extend grounding continuity as you've suggested to include the body of the machine?

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: 480 - 240V Transformer check.

I agree with David.
In Canada (And probably the US) grounding the neutral is a code requirement at that voltage.
Look for a 240 Volt secondary. 480:139/240 Volts.
More common is 480:120/208 Volts. That may be a little low foe your machine.
The problem connection is the grounded wye/delta connection. The four wire primary connection locks in the phase angles and voltages and the delta secondary is unable to willingly accept any unbalances.
With the delta/delta the angles and voltages are not constrained and the secondary is free to track primary unbalances.
If you are unable to locate a delta/wye transformer with acceptable voltages, your second choice may be two 480:240 Volt ransformers in an open delta configuration.
Third choice may be a 480:120/240 Volt four wire delta with the center tap grounded.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 480 - 240V Transformer check.

If you can find a 480 delta / 138/240Y that would be ideal, but if not a 480 delta / 120/240 delta side tap (more readily available) is the next best option. Just make sure you use breakers that are straight rated and not slash rated. Mark the high leg if you go the 120/240 route.

http://www.practicalmachinist.com/vb/attachments/f...


In the US you could go delta ungrounded, but you need a ground detector and in all honesty its best not to bother.

Some machines like VFDs do not life floating voltages- or one leg elevated- so make sure you double check that if you go the delta route.

RE: 480 - 240V Transformer check.

I believe you need to carry a ground, but not the neutral. Also the grounded lead can be used for detecting a ground in the machine.

RE: 480 - 240V Transformer check.

Correct, for a straight 230 volt machine. 133/230 would need a neutral.

RE: 480 - 240V Transformer check.

If there are VFDs or servos fed from 3 phase 240V in the machine, absolutely go find the Wye secondary. 3 phase bridge rectifiers in most modern drive systems will have issues with being fed with a delta source. 240 Y transformers are not standard for distribution because of the 139V L-N voltage, but they are often available as "drive isolation transformers".

If there are no 3 phase rectifiers involved, I wouldn't use the non-standard voltage, because Murphy dictates that some future goober will read 240V L-L and ASSume it is 120V to N, then fry something.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: 480 - 240V Transformer check.

@Jraef: Exactly what I had in mind. Agree 100%. :)

RE: 480 - 240V Transformer check.

jraef, In such cases the secondary Y neutral is not earthed. That is the standard in solar inverters seen in my area.

RE: 480 - 240V Transformer check.

prc: Are the solar inverter systems back feeding a delta:wye transformer?
That is, power in to the wye side and power out the delta side.
That is a special case that often leads to issues in practice.
The issues may be avoided by floating the wye point.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 480 - 240V Transformer check.

(OP)
Nice consensus! The machine is mostly VFDs and drive fed motors so we're on the hunt for a wye output.

Indeed 240 wyes are not common. Most of these machines are actually made with a nameplate supply number of 220V. Which gets you into 'trying' 208V. Some are tolerant and don't care but others monitor the voltage and 'tilt' if it drops much below. What happens is when the machine starts a non-VFD'd motor like a coolant pump or hydraulic chiller it causes a brief dip that is enough to cause the already low 208V to dip below the trip and the controller stops on an error which requires human intervention to continue.

Thanks all.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 480 - 240V Transformer check.

jraef,Yes.Power is fed from Y to delta and the neutral of Y is kept floating. In one case where it was earthed by mistake, inverters started failing.
'That is a special case that often leads to issues in practice.
The issues may be avoided by floating the wye point.'- can you explain this a bit more? Why modern inverters find delta source not compatible?

RE: 480 - 240V Transformer check.

How many Amps do you need Keith?
Probably the most available transformers will be 480:208/120 Volts.
You can use three three small 120:12 Volt or three 120:16 Volt transformers to boost the line to line voltage to 228 Volts or 236 Volts.
The current rating of the 12 Volt or 16 Volt windings need only be 1.73 times the needed current.
Yes, it's a little kludgey but it may be what is available at a reasonable price.

The other option may be the delta:delta with a four wire 124:240 Volt secondary with a "wild leg and a grounded center tap.
jraef; How do VFDs respond to a high leg system. The voltages to ground will be 120V, 120V and 208 V.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 480 - 240V Transformer check.

(OP)
Transformers on transformers. Too kludgey Bill :)

Kinda sad cuz the place has a ton of 460 drops everywhere but 90% of their machines are 220V. I'd prefer just switching all drops to new machines over to 240 but then the wire is probably too small, but then the conduit probably can't stand the bigger wire, so now you have to yank a bunch of 250 foot runs of conduit off a 40 foot ceiling and replace it all with larger everything.

So the solution seems to be putting a transformer next to each machine so you can heat the local space, trip over the dang things, and have to make more room for them.

Non-optimal - painted gold.

Keith Cress
kcress - http://www.flaminsystems.com

RE: 480 - 240V Transformer check.

I see some possible code issues.
I don't work with the NEC but there is a lot of similarity with the Canadian Code.
I realize that the Canadian Code does not apply but hopefully someone will supply the NEC equivalent.
There are significant differences between equipment grounding conductors and system neutral grounding conductors.
In Canada if a grounded neutral of a system results in voltages to ground of 150 Volts or less then the neutral must be grounded.
A delta:wye transformer would be considered a separately derived system and would require a system ground. It is doubtful that the equipment bonding conductor will meet code for a system ground. The installation requirements for a system grounding conductor are more stringent than the requirements for an equipment bonding conductor.
The nice fix voltage wise is a two transformer open delta auto-transformer connection.
The voltages to ground will be 277 Volts, 139 Volts and 139 Volts.
The advantages are:
Cheapest.
Smallest.
Does not require a neutral.
Does not require a system ground.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 480 - 240V Transformer check.

Keith,
As I said, the way to find these transformers that will have a 230V Y secondary is to look for "Drive Isolation Transformers". In the following linked document, see page 5 of the PDF (referred to as page 127), part #DM040JC

http://www.hammondpowersolutions.com/files/HPS-Sta...

Pretty much ass of the major transformer mfrs offer similar products, you just need to look in the right places.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: 480 - 240V Transformer check.

Jeff; As a separately derived system, will the NEC require a system ground rather than an equipment ground on the secondary wye point?
In many Canadian plants an additional system grounding conductor would have to be run to remote mounted transformers in addition to an existing equipment grounding conductor.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 480 - 240V Transformer check.

Yes, the secondary Wye point must be grounded. That's another benefit of using a Wye secondary, because for a Delta, it would need to either be corner grounded, or have GFP added.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: 480 - 240V Transformer check.

Thanks for the information, Jeff.

Quote (OP)

so now you have to yank a bunch of 250 foot runs of conduit off a 40 foot ceiling and replace it all with larger everything.
In Canada, these conduit runs would either have equipment bonding conductors or in some instances the conduit may serve as the bonding conductor.
Our code allows normal splices in bonding conductors but is very restrictive of splices in system grounding conductors.
The sizing criteria is also different.
In most plants we would have to run new system grounding conductors to meet code.
Hence my question regarding the effect of voltages to neutral/ground of 277V, 139V, and 139 Volts.
Your solution is the acknowledged best way to go in most instances Jeff.
However, if Keith is faced with running hundreds of feet of system grounding conductors, it may be well to investigate the usability of an alternate solution.
Another option may be to use three transformers connected as wye autotransformers. This would give 240 Volts with equal voltages from line to ground.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 480 - 240V Transformer check.

IEEE standard for solar transformers C57.159-2016 where under clause 5.1.4 quote -The inverter operation is not affected by the inverter transformer vector group (Dy1, Dy5, or Dy11 will make no difference). No neutral connection is required on the primary (LV) side of the transformer. If a neutral point of the primary (LV) winding is available, it is recommended that this neutral point is neither grounded nor connected to other ground points. On the secondary (HV) side, the inverter transformer can have an isolated neutral point or resonant grounding or low resistance grounding -unquote

RE: 480 - 240V Transformer check.

This looks like two issues combined in one paragraph.
Issue #1.
The vector group does not matter.
Issue #2
Grounding the wye point, if available.
This mentions possible wye points on both the primary and the secondary sides.
Dy1, Dy5, and Dy11 do not have a neutral on the primary side.
Thank you, prc, for bringing this recommendation to our notice:

Quote (IEEE)

If a neutral point of the primary (LV) winding is available, it is recommended that this neutral point is neither grounded nor connected to other ground points.
Note: If a wye:delta configuration must be used for special circumstances, it is strongly recommended that the primary wye point be left floating.
This applies to any installation, not just solar installations.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 480 - 240V Transformer check.

Waross, in all those combinations HV is usually delta connected. Only LV where power is fed is star and the neutral will be floating. This is opposite to normal step up transformers where power is fed to delta LV and HV star neutral is earthed.(YNd1 or Ynd11)

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close