Electric vs. pneumatic deluge valves

Electric vs. pneumatic deluge valves

(OP)
Hello everyone,
I've been looking into deluge valve manufacturers but I'm not clear on the application difference between models that operate solely with electric solenoid actuation and those that have electric solenoid pneumatic actuation. At first view it would seem that pneumatic actuation requires a more complicated arrangement, but what are the advantages?

RE: Electric vs. pneumatic deluge valves

The pneumatic units need a separate air supply to operate. The hydraulic units use the water supply pressure to operate.

http://www.singervalve.com/deluge-valves

RE: Electric vs. pneumatic deluge valves

Hi juanjogo!

Basically there are two types actuation systems for Deluge Valves:
1. Pneumatically Actuated DV and
2. Hydraulically Actuated DV.

1. Pneumatically Actuated DV:
In these types of DV there is a separate Quartzoid Bulb Detection(QBD) System and spray nozzle network. On reaching the rated temperature the bulb fuses and the pressure in the pneumatic tube drops which allows the DV to open and thus enabling water flow through the spray nozzles.

2. Hydraulically Actuated DV:
In this case the QBD system is integrated with nozzle and is known as Sprinkler system. There is no need of separate pneumatic tubing network. On reaching the rated temperature the bulb fuses and the pressure in the network drops which actuates the pilot line connected to DV via main line and allows DV to open.

Thanks!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close