100% reactive load on transformer.

100% reactive load on transformer.

(OP)
I have a problem with a supply. One side of the supply is a connection of two users on a private grid and a generator on one (secondary) side of a transformer (1000V). The primary side of the transformer is connected to official grid (230V). On certain loads the active power transformer is close to zero, but the reactive power is high (i.e. ratio 2:40). The reactive component is for magnetizing the generator and the active power is net supply to official grid.
The MMCB on the primary side is set to 200A, and keep on tripping after just a few minutes. Instability in transformer? I hav installed a capacitor battery at the generator. When logging currents (capacitor, generator and line current from generator) at 2 seconds interval, all currents are stable. Anyone seem this before?

RE: 100% reactive load on transformer.

Is this a new installation or an existing one?

Is this a single-phase or three-phase installation?

What transformer winding arrangement do you have?

What size generator and transformer are you dealing with?

RE: 100% reactive load on transformer.

Induction generator?
There is so, so much that you didn't tell us.
Is this a new breaker or one that was sitting around?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: 100% reactive load on transformer.

Amps are amps, reactive or not. a standard CT or a clamp-on ammeter will tell you what the current is. If it exceeds the trip setting of the breaker or an overcurrent relay, it's going to trip.

That's the way things are supposed to work. Heat buildup in cables and other apparatus is based on current.

old field guy

RE: 100% reactive load on transformer.

You may be having a harmonic resonance problem among the capacitor, generator, and transformer. If you have a source of harmonic current at a resonant frequency, there may be high harmonic currents. If you logging meter does not measure true rms current, it may not show the full current.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close