telecommunication tower: lower leg reinforcement
Tower leg is overstressed by around 10% and bracing can not be added nor reducing antennas loading.
any proposals?
any proposals?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
RE: telecommunication tower: lower leg reinforcement
How to strengthen the legs at the lower panel noting panel is 3m and the legs are braced at 50cm interval
Regards.
unfortunately we can not encase the leg as we have to keep anchor bolts/bracing/etc.exposed for maintenance.
any sketch/calculations on how to strengthen the leg
If so, you can stitch weld plates to the outside face of the angle legs, increasing the area and section modulus. should be a straightforward calculation to check the increased axial capacity. if the over stress is only 10% a 6 to 8mm plate should do it.
if so the leg will have non uniform section how to proceed/or may be I'm missing something?
Similar method for a four legged tower, only can use off the shelf angles.
Will gave to do some grinding for a tight fit...
Mike McCann, PE, SE (WA)
Dik
Initially, what concerned me about this strategy was the relative impermanence of the set up. I've relaxed on that since. Really, any determined vandal with a wrench could probably find a way to disassemble one of these towers with or without reinforcement.
is it a column failure (which would be helped by mid-span reinforcement) or simple brute force (ie the ground reaction, which need to reinforce the ground attmt point) ?
It looks like a four poster to me (the far post is inline with the near one, but I think I can see the far footing).
Why is it impossible to add additional legs if reinforcing the existing legs doesn't work ?
How did this thing get to be 10% down ?
Thanks any way
dik;and
msquared48
in case bolted solution adopted did you add reinforcement in the base shoe vicinity (typical photo from other tower is attached).
Any actual examples/some sketches/or refrences/etc..
Regards.
for the U bolts option do you have any references for such design
and references to verify U bolts size/spacing/etc..
Thanks for your time
is it unreasonable to add feet, like another four on a diagonal diamond pattern ?