Hi Folks,
I have a Supply Fan Delivering 22,500 CFM of Supply Air. A Return Fan bringing back: 20,200 CFM. And a washroom exhaust fan in the space exhausting 1000 CFM.
To Summarize:
SA: 22,500 CFM
RA: 20,200 CFM
Washroom Exhaust: 1000 CFM
What is my Outdoor Air rate?
I have a Supply Fan Delivering 22,500 CFM of Supply Air. A Return Fan bringing back: 20,200 CFM. And a washroom exhaust fan in the space exhausting 1000 CFM.
To Summarize:
SA: 22,500 CFM
RA: 20,200 CFM
Washroom Exhaust: 1000 CFM
What is my Outdoor Air rate?





RE: Outdoor Air Rate Determination
TTFN (ta ta for now)
I can do absolutely anything. I'm an expert! https://www.youtube.com/watch?v=BKorP55Aqvg
FAQ731-376: Eng-Tips.com Forum Policies forum1529: Translation Assistance for Engineers Entire Forum list http://www.eng-tips.com/forumlist.cfm
RE: Outdoor Air Rate Determination
RE: Outdoor Air Rate Determination
Bill
Engineering Professionals, Inc.
RE: Outdoor Air Rate Determination
For your case The outdoor air = 22500 SA - 20,200 RA = 2300 CFM
Confirm if this OA is adequate for ventilation and for sum of exhaust + pressurization.