How close tolerance does a run capacitor have to be?

How close tolerance does a run capacitor have to be?

(OP)
There is a discussion with a guy that says his air conditioner fan motor over heated and died because the manufacturer used a 7.5uF instead of the 5uF as stated on the motor. This motor has a run and a start capacitor. I think the cap just opened up or the bearings started to freeze. A friend lets me scavenge old HVAC units for parts and I've seen higher value caps on motors before. Someone told him that the cap has to be within 10% or the motor greatly overheats. I've always thought a little higher was better than being under. Certainly that much higher wouldn't damage the motor. The manufacturer must do it for some reason. Just curious.

RE: How close tolerance does a run capacitor have to be?

Generally the manufacturer will use the smallest capacitor he can get away with to minimise costs. In my experience larger caps just cost more, never heard of a motor dying as a result of using one.

RE: How close tolerance does a run capacitor have to be?

Generally a run capacitor does not affect the motor at all. It affects the KVARs drawn from or delivered to the grid,and affects the power factor but it does not have a direct affect on the motor.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: How close tolerance does a run capacitor have to be?

Thought a run capacitor gives a motor greater torque capability since it keep the start winding partly energized while running.

RE: How close tolerance does a run capacitor have to be?

Hi Compositepro. I stand corrected. I was thinking three phase motors.
A capacitor in series with the start winding should ideally shift the phase angle of the start winding current to coincide with the physical electrical angle that the start winding is offset from the run winding.
However this shift is not 90 degrees from the applied voltage but 90 degrees from the normally lagging current of the run winding.
In addition, the phase angle of the run current will shift with the degree of loading.
I suspect that the motor manufacturer spec'ed the minimum value of capacitor to run the motor and the A/C manufacturer used the optimum size for their application and fan load.
The wrong value run cap may cause overheating of the motor, but the more likely cause of burn-out may be bearing failure, start capacitor failure, or starting relay failure.
If the oversized cap caused the burn-out, I would expect an early failure. Warranty claims would be expensive.
How old is this unit?
Is it possible that the capacitor has been replaced in the past with the wrong value?
Can the wrong value capacitor cause motor heating? Yes.
Is a jump from 5 uF to 7.5 uF enough to cause over heating? Probably not.
Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close