Hi all:
In our property We have been having mechanical seal failures that in my opinion are excessive.
Since most of the systems are still under DLP, I'm arguing that given the high rate of failure, the contractor assumes the cost of an entire full replacement before DLP expires to be validated by pump manufacturer, which he is trying not to do due to the costs involved.
I was trying to find some indications on expected life expectancy on mechanical seals, but I can't find anything definitive. What I know is that given that these pumps are basically pumping water for HVAC and compared with my past experience in chemical industry, these mechanical seals are presenting an abnormal rate of failure.
Let me give you some numbers:
From 5 condensing water pumps, 4 had its mechanical seal replaced between 10-14 months after put into service
Chilled water: 1 out 5 in 14 months of service
Evaporator side on the heat pump: 2 out of 3 in 9 months of service
Hot water @80C 6 out of 8 failed within 9 months
Hot water @60C: no mechanical seal failure up to now out of 10 pumps
All pumps are from the same manufacturer (Grundfos)
I know that the life expectancy of a mechanical seal depends on a lot of factors namely type, fluid, pressure, temperature, etc. but I was hoping to find some industry rules of thumb (or ideally something more concrete) that I can nail the contractor with or else I'm seeing myself having him walking away in a couple of months when DLP expires and I stay with all the lemons to make a big sour lemonade...
Thanks a lot for your feedback.
In our property We have been having mechanical seal failures that in my opinion are excessive.
Since most of the systems are still under DLP, I'm arguing that given the high rate of failure, the contractor assumes the cost of an entire full replacement before DLP expires to be validated by pump manufacturer, which he is trying not to do due to the costs involved.
I was trying to find some indications on expected life expectancy on mechanical seals, but I can't find anything definitive. What I know is that given that these pumps are basically pumping water for HVAC and compared with my past experience in chemical industry, these mechanical seals are presenting an abnormal rate of failure.
Let me give you some numbers:
From 5 condensing water pumps, 4 had its mechanical seal replaced between 10-14 months after put into service
Chilled water: 1 out 5 in 14 months of service
Evaporator side on the heat pump: 2 out of 3 in 9 months of service
Hot water @80C 6 out of 8 failed within 9 months
Hot water @60C: no mechanical seal failure up to now out of 10 pumps
All pumps are from the same manufacturer (Grundfos)
I know that the life expectancy of a mechanical seal depends on a lot of factors namely type, fluid, pressure, temperature, etc. but I was hoping to find some industry rules of thumb (or ideally something more concrete) that I can nail the contractor with or else I'm seeing myself having him walking away in a couple of months when DLP expires and I stay with all the lemons to make a big sour lemonade...
Thanks a lot for your feedback.





RE: Mechanical seal failures
It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
RE: Mechanical seal failures
Only am organisation who see hundreds of pumps per year will have the statistics you're looking for.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Mechanical seal failures
Has the contractor set up and applied a selection process for the procurement of the seals or was it left up to the pump manufacturer?
Has the contractor prepared a technical specification for the selection of the mechanical seals? and/or has the end user put some project requirement on the selection of the seals?
RE: Mechanical seal failures
RE: Mechanical seal failures
RE: Mechanical seal failures
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Mechanical seal failures
RE: Mechanical seal failures
As far as I know, since I'm part of the operations team, and not the construction, all pumps and mechanical seals were supplied by Grundfos but I'll try to get some more information about it.
Of course at this stage of the game, I doubt that the contractor will be very forthcoming on sharing information with me.
Let's see where this takes us.
RE: Mechanical seal failures
Return a few of the failed seals to Grundfos for comment.
It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
RE: Mechanical seal failures
http://turbolab.tamu.edu/proc/pumpproc/P17/P17171-...
RE: Mechanical seal failures
That's what we are doing. We are requesting Grundfos to step in and give us a technical assessment of the root causes for premature seal failures.
rotw:
Thanks for the article I scrolled it quickly and it gives some nice information. I'll read it more carefully tonight at home when everybody is asleep and I can dig deeper on those calculations.