Earth fault protection high impedance grounding
Hello Dear Colleagues,
I have a 4,16 kV industrial switchgear with high impedance grounding through a ZigZag transformer limiting fault current to 50 A.
Unfortunately the MV metalclad switchgear came without zero sequence CTs and some phase CTs have a high ratio 2000/5 limiting both sensitivity and speed as fast trip times cannot be achieved without compromising security under transients such as transformer energizing and motor starting.
I have opted for maintining a good sensitivity (about 10 A primary) at the expense of speed with delays of 1 -2 seconds in order to deal with the errors of residual measurement.
The fault current itself is not dangerous and I think we are still tripping in a reasonable time to avoid a single phase fault evolving into multiphase although as far as I know this is less likely for a 4,16 kV system than for higher voltages.
I appreciatte your comments on the issue and if there is a guide with recommendations for earth fault protection settings in this kind of systems.
Charlie
RE: Earth fault protection high impedance grounding
Hi Charlie,
Any chance of retro-fitting zero-sequence CTs into the switchgear? I don't see a retro-fit as a big-deal, plus I really think that with a 50A resistor you might not be able to achieve the desired sensitivity and coordination with only residual protection. Do the existing PRs have zero-sequence inputs, if so all you need to install (per cell) is one CT and two wires. Piece of cake.
I guess that the resistor is non-continuous rated (ie 15 to 30s). That implies that you will have a towering inferno if your residual protection fails, correct?
GG
"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)
Hi GroovyGuy,
Thanks for your reply. Indeed retrofitting would be the best solution but we are dealing with Oil&Gas industry and managers will not be willing to invest and lose production to improve GF protection. We have to find a solution with what we have in hands.
All protection devices do have a ground CT input. My main concern is not sensitivy, I could go to 10% or 20% of maximum GF current even with 2000 A CTs (the PR allow that sensitivity). My main concern is tripping time. I have to use long delays to cope with large CT errors during transients.
Charlie
Hi Charlie,
I too work in the O&G industry, so I realize how tough it is to find money lying around. I think that, as you have suggested, that a trip point of 10A at 1-2s should be adequate.
However, I wouldn't give up on trying to convince management that the zero-sequence CTs are a good thing. What you are trying to achieve may be doable, but I have never seen it done before. Better to take your lumps now, rather that later should it hit the fan.
GG