Min. Clearances for Utility Crossings

Min. Clearances for Utility Crossings

(OP)
I'm involved in a project, where an engineer wants to install a new storm pipe in a nest of existing utilities. The new pipe would cross 6" above an existing duct bank (no idea how many volts it's carrying) and an existing water main, and it would cross 8" below an existing gas line.
I'm trying to find standards on the minimum allowable clearances for crossings. The NEC didn't seem to have anything regarding the ductbank (or maybe I missed it), and I'm not sure where else to look. Thanks!

RE: Min. Clearances for Utility Crossings

Check with the utilities affected...

Dik

RE: Min. Clearances for Utility Crossings

(OP)
Thanks. Unfortunately, this is an "emergency", and there's not much time to do that.
Appreciate your help, and I agree that would be the best thing to do.

RE: Min. Clearances for Utility Crossings

It'll be more of an emergency when the gas utility makes you take everything out.

RE: Min. Clearances for Utility Crossings

I had buried pipe crossing about 2 inches gap over existing pipes. Added styrofoam in between to ensure that no direct load on the duct bank or pipe.

RE: Min. Clearances for Utility Crossings

Quote (jgailla)

It'll be more of an emergency when the gas utility makes you take everything out.
Depending on whose right-of-way it is, licensing agreements, easements, etc.; the onus may be on the gas utility to take everything out.

Similarly, the clearances are likely set by the owner of the property on which the utilities run. Are these public or private?

RE: Min. Clearances for Utility Crossings

(OP)
Public. The storm pipe would go under a 4" gas main, with about 8" of clearance.

RE: Min. Clearances for Utility Crossings

(OP)
Everyone, thanks for your help!

RE: Min. Clearances for Utility Crossings

Gas and oil pipelines need a minimum clearance of 12" to ANYTHING.
Crossings with electric cables, underground or overhead, need to be as near perpendicular as possible and should never run parallel in close proximity.

Check in with your state's ONE CALL SYSTEM before beginning excavation work near any pipeline ... or buired electric cable.

Gas companies normally will require their rep/inspector to be present during any excavation near their pipelines. Convince them that it's an emergency.



Technology is stealing American jobs. Stop H1-Bs for robots.

RE: Min. Clearances for Utility Crossings

In some areas it is leaglly required for you to check out the utilities if you are anywhere near them.

RE: Min. Clearances for Utility Crossings

(OP)
BigInch, can you give me a standard to cite?

RE: Min. Clearances for Utility Crossings

How large of a storm drain are we talking?

Have you considered using elliptical pipe, or 2 smaller pipes to get you the clearance you need? If thick walled reinforced concrete pipe is being used, could you use PVC instead? That could get you upwards of four additional inches of clearance, top and bottom.

RE: Min. Clearances for Utility Crossings

From experience, when dealing with storm drains of that tight a clearance, make sure you take pipe thickness into account. Civil designs for storm drain are based on the interior dimensions of the pipe, not the exterior.

Hydrology, Drainage Analysis, Flood Studies, and Complex Stormwater Litigation for Atlanta and the South East - http://www.campbellcivil.com

RE: Min. Clearances for Utility Crossings

Yes, the references are ASME B31.4 & B31.8 which state the 12" clearance for liquid hydrocarbon and gas pipelines, respectively. The legal requirements in the USA for federally regulated pipelines are (the 2002 edition of those documents) namely, the Code of Federal Regulations Title 49 Parts 192 and 195. Distribution company gas pipelines commonly found in city works will not usually be federally regulated, so they won't actually be covered under the CFRs, but that wouldn't necessarily be an excuse for not following customary practices established by precedence under USA federal law, hence Southwest Gas' 12" clear reguirement that was mentioned by cvg above.

Technology is stealing American jobs. Stop visas for robots.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close