Power Formula for 3phase 115v 400Hz motor Y connection I think.
Is it.....
a) P=Sqrt(3)*E*I*cos(theta)
b) P=3*E*I*cos(theta)
Can anyone explain the difference?
Regards,
Is it.....
a) P=Sqrt(3)*E*I*cos(theta)
b) P=3*E*I*cos(theta)
Can anyone explain the difference?
Regards,
Edson Campos





RE: Power Formula for 3phase 115v 400Hz
In (a.) E = ø-ø voltage.
In (b.) E = ø-n voltage.
Both are assumed to be balanced conditions.
RE: Power Formula for 3phase 115v 400Hz
regards,
Mark Empson
http://www.lmphotonics.com
RE: Power Formula for 3phase 115v 400Hz
Notice that the power will be the input power not on the shaft side since the motor efficiency is missing in those equations.
Equation a. can be used for delta or wye motor connection.
Equation b. is more linked to wye motor connection since the phase to neutral voltage is involved.
RE: Power Formula for 3phase 115v 400Hz
Now is (theta) 120 degrees and if not how do I find out what it is?
Reagards,
Edson Campos
Edson Campos
RE: Power Formula for 3phase 115v 400Hz
If you need something exact, you will have to measure the power factor, or get a plot of power factor vs load from motor manuf.
RE: Power Formula for 3phase 115v 400Hz
Or you can try: watts in
---------
1.732 x V x A
Hope this helps...
P.
x103
RE: Power Formula for 3phase 115v 400Hz
AND equation b would only be applicable for a WYE connected motor. It would NOT be correct for a delta connected motor.
A dangerous equation to use.
RE: Power Formula for 3phase 115v 400Hz
Oops, you're after power [watts] not power factor - my bad.
RE: Power Formula for 3phase 115v 400Hz
In the real world I assume 400 Hertz to be a VSD. VSD controllers offer both a variable torque and constant torque operation. In a constant torque operation they offer a function that is called "extended speed range." In the extended speed range kW still equals 746 kW per HP more or less, but the actual KVA gets very confusing. If you increase the current and frequency while holding the volts constant the drive or motor KVA required is a problem!
That's probably why they have an overload function built into a VSD.
David
RE: Power Formula for 3phase 115v 400Hz
cos(theta) is defined between and including 0 and 1 since there is no passive element causing a lag or lead greater than 90 degrees.