Wind load on covered pipe bridge

Wind load on covered pipe bridge

Wind load on covered pipe bridge

(OP)
I got a pipe bridge that consists of a couple of 10' x 10' towers supporting what is essentially another 10' x 10' "tower" (running horizontally). Basically the frame is all HSS members. It is very stiff as there are HSS members running between the columns bracing it up. (Almost like a lattice tower except they are connected by welding).

I am uncertain of the wind loading to apply. If it was uncovered with deck.....the answer would obviously be loading it on a member by member basis or per "Signs & Lattice Frameworks" provisions in Figure 29.5-2 in ASCE 7. However, since this thing is completely covered in deck, I'm unsure as to whether to treat is like a enclosed structure, use the provisions in Figure 29.5-1 (i.e. a chimney, tank, or rooftop equipment), or perhaps even treat it like a sign (i.e. the provisions in Figure 29.4-1).

Your thoughts?

RE: Wind load on covered pipe bridge

Sounds very much like a sign structure to me. Sort of like an overhead highway signage gantry.

RE: Wind load on covered pipe bridge

(OP)
It kind of reminds me of a sign as well. I'm just having my doubts because it's not thin like a sign.

RE: Wind load on covered pipe bridge

is the 10'x10' totally enclosed by cladding?...if it is, I would treat it like horiz ductwork with Cp of 1.3..

RE: Wind load on covered pipe bridge

(OP)

Quote:

is the 10'x10' totally enclosed by cladding?

Yep. Except for the ends. (So the pipe can run.)

Quote:

if it is, I would treat it like horiz ductwork with Cp of 1.3..

Good point.

RE: Wind load on covered pipe bridge

on further thought, just in case the OP is designing to a knat's eyebrow, make that a Cp=1.4, 0.8 windward, 0.6 leeward...

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources