Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

(OP)
What would be the effects and measures that would need to be taken if a transformer is replaced with one having lower impedance (6.22 % with 6 %)?

RE: Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

More fault current and better regulation. 6% and 6.22 is low. I have seen industrial setups where someone had specified too low of an impedance and a choke needed to be installed downstream to avoid needing to upgrade the switchgear to meet the fault duty.

Shouldn't be much difference to go from 6.22 to 6. Probably, just need to check relay coordination and available fault current, which probably has changed since the relaying Was last set.

RE: Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

'Low' is subjective though - we don't know how big this transformer is.

RE: Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

(OP)
@ScottyUK its a 2.5 MVA 11kV/0.4 kV dry type transformer.

RE: Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

At 6.22% impedance your available fault current will be 58013 Amps.
At 6% impedance your available fault current will be 60140 Amps.
The change in regulation may not be proportional to the change in impedance.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

Depending on the change in X/R of the impedance regulation could be either better or worse; no way of telling from just the impedance magnitude.

RE: Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

I think it is not an issue. In a batch of transformers, there can be that much difference among units.

RE: Effects of replacing an existing Dist. Transformer with one having lower % impedance (6.22 with 6.0)

In Europe most breakers capable of handling the output of that transformer will have at least 65kA breaking capacity, so the effect on equipment should be negligible.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close