Why cannot we put Chiller and Fire electric pumps on same ACB?

Why cannot we put Chiller and Fire electric pumps on same ACB?

(OP)
Hello!!

My senior engineer asked me that, Why cannot we put Chiller and Fire electric pumps in same ACB?

Can we connect both on the same ACB or not. If No, then why cannot we. Please advise on this.

RE: Why cannot we put Chiller and Fire electric pumps on same ACB?

What country, what legislation are you working to?

RE: Why cannot we put Chiller and Fire electric pumps on same ACB?

(OP)
Working in Dubai, united arab emirates. providing services to hospitality industry.

RE: Why cannot we put Chiller and Fire electric pumps on same ACB?

What if your chiller motor catches on fire and trips the ACB?


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: Why cannot we put Chiller and Fire electric pumps on same ACB?

I find it a little funny that this question is for a project in Dubai with its reputation for building fires.

RE: Why cannot we put Chiller and Fire electric pumps on same ACB?

(OP)
hahaa!! first of all @hamburgerhelper, it is not a project. It was just a question asked by senior. And I agree with @jraef but there must be some other reason as well, which would relate this to the "Art695" fire system electrical wiring codes...
Or may be something else!

RE: Why cannot we put Chiller and Fire electric pumps on same ACB?

Sounds like a code-specific question for Dubai, but fire pumps are generally provided with minimal protection to give the pump the greatest chance of operating under fire conditions.

RE: Why cannot we put Chiller and Fire electric pumps on same ACB?

(OP)
This is what I was expecting and being confused between.. thank you @ScottyUK

RE: Why cannot we put Chiller and Fire electric pumps on same ACB?

In addition to that "run to destruction" aspect, you also use a dedicated circuit for the fire pump so that nothing else takes it off line. That's what my comment was referring to.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close