Anyone know of a good meter to measure, adjust & monitor PF for such an application?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
Power Factor Meter for 200 KW grid tied generator
|
RE: Power Factor Meter for 200 KW grid tied generator
1) What do you have in terms of PTs and CTs?
2) Does you exciter controls not presently control pf? What is the make /model of this controller (or is it embedded into the main generator controller)?
3) Where is setpoint coming from for this new pf controller?
4) Do you currently have a digital power meter associated with the gen-set? If so, make & model svp?
"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)
RE: Power Factor Meter for 200 KW grid tied generator
It's a 2400 V, 3-Ph generator - 2-20:1 PT's & 3-CT's. PF/VAR controller is an older Basler (analog) SCP 250. I suspect it's doing a decent job but need it has no output so there's no way to tell.