Compressed air pressure for valves
I am wondering, what is a common range of air pressure required to actuate control valves? Butterfly and globe.
Thanks!
Thanks!
Compressed air pressure for valvesCompressed air pressure for valves(OP)
Thanks! Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesThe world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
Engineering-centric businesses face a number of challenges today, but unmanageable design and change processes don’t need to be counted among them. Download Now
RE: Compressed air pressure for valves
- Higher air pressure allows the use of smaller, less expensive valve actuators.
- Higher pressure provides more motive force for faster response time from the control valves.
- Higher pressure minimizes the pressure fluctuations that are experienced in the instrument air system, thus preventing occasional sluggish response from some of the valves.
I suggest operating your instrument air at about 100 psig, but consult with an instrument engineer on this.RE: Compressed air pressure for valves
"21.2 Air supply system
For proper unit instrumentation operation, instrument air shall be ... at minimum pressure of approximately 100 psig (700 kPag) at the inlet to instruments air header.
21.2.11 Distribution system
Lines in the distribution system should be sized a manner that the maximum pressure drop between the dryer outlet and the most remote consumer does not exceed 5 psi (35 kPa) when all consumers are taking air at maximum rates."
All it means 665 kPag at the inlet to control valve's actuator.
So looks like we usually deal with up to 100 psi, and that would be for a small actuator. 40-60 psi for a larger one.
Thanks everyone!
This relatively low air pressure did require the use of large (~12" diameter) rolling-diaphragm valve actuators.