This should be a quick one:

For Medium Voltage applications, lets say I have a 2.6MW generator and I need to size the cable for this.

I normally go 2.6MW / 0.8PF to give me 3.25MVA (worst case PF, they typically run at 1PF).
And then go 3.25MVA / root3 / 4.16kV = 451A.
And then on top of that I add the 125% factor to give me 563A for minimum cable ampacity.

My colleagues say, that since you are already including a safety buffer in the 0.8PF, you don't need to add the 125% additional safety factor anymore....

I disagree, b/c the PF during operation can range anywhere between 0.8 to 1.0. So you can't rely on that for cable ampacity calcs.....

Thoughts?

RE: Cable Sizing for Generators: 125% Rule vs. PF

0.8 is worst case PF. So 1.0 should give you less cable load - not more.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Cable Sizing for Generators: 125% Rule vs. PF

The rated current of a generator is based on KVA/MVA, not on kW/MW.
The maximum allowable current is at .8 PF
This is not a safety factor. It is the maximum possible load.
Then add 125% safety factor as you do.
You are correct.
In North America the code requires 125% of rated current. That is current at 0.8 PF X 125%.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Cable Sizing for Generators: 125% Rule vs. PF

Taking the amperage rating of the set from the nameplate and multiplying by 1.25 would likely be the simplest and safest way to do it. The calculation you presently do is the next best way.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close