HVAC Control Conflict

HVAC Control Conflict

(OP)
Hi all, I have a situation where I have a switchgear building which is located within the reach of a gas cloud. We are not able to locate the building away. The HVAC system intake damper will close in the event of 30% LEL to prevent gases from being introduced into the building. On the other hand, the building requires pressurization to be maintained which requires air intake. Hence, there is control conflict. In this case, I am hoping anyone had the same situation and was able to mitigate by engineering controls and share them. Worst case we want to avoid is to shutdown the electrical building. Thank you in advance.

RE: HVAC Control Conflict

You may have to duct-in make-up air from outside the hazardous area.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: HVAC Control Conflict

howdy,
Bill is correct; you need a clean source of pressurization air brought into the bldg. This is a typical solution to a common problem. If your gases are heavier than air, an 20ft length of vertical ducting is all that is required to get at a clean source of air.

You also should have redundant LEL xmitters located within the electrical room. 30% is too high in my opinion, you should alarm @ 10% and shutdown at 20%.

API-505 has some good info wrt this type of solution.

GG

"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)

RE: HVAC Control Conflict

Look into molecular sieve for emergency makeup air when gas is detected. Seal the room well so low makup air is needed.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close