How to perform temperature sensor calibration at site ?

How to perform temperature sensor calibration at site ?

(OP)
How to perform Temperature Transmitter and temperature gauge Calibration at Site ? What are the tools required to perform calibration of RTD OR Thermocouple ?

RE: How to perform temperature sensor calibration at site ?

To what level of precision?

Google "dry block calibrator" - probably one of the more portable methods. Precision will not be comparable with a lab-grade platinum RTD, but you should be able to find calibrators to get within 1 deg. C of error or less.

RE: How to perform temperature sensor calibration at site ?

As mentioned depends on what level of precision, how many points and perhaps what's available/conditions at the test site.....

In my past career with the thermocouple system we used to instrument equipment under test with a number of test points of interest, while undergoing a THA test cycle, an initial reference check with all thermocouples in an ice/slury mix to check calibration at 32F was sufficient. e.g. http://www.thermoworks.com/learning/thermapen101_c...

RE: How to perform temperature sensor calibration at site ?

Ice slurry as Dan says and boiling water for another point.

RE: How to perform temperature sensor calibration at site ?

If you have a thermowell adjacent to the RTD you can insert a (calibrated) temperature probe and check they are reading within 0.5 degC of one another. As for the transmitter you can inject a resistance at 5 points across the range of the transmitter and measure the output which you compare against the expected output ensuring the %error is within spec.

RE: How to perform temperature sensor calibration at site ?

I have never seen a dry block calibrator used on site, it would be too slow in fact I'm not even sure I've seen one in an instrument shop, more of a teaching tool.
A decade box is used for RTD, you cannot adjust the probe only the transmitter.

A thermocouple calibrator for thermocouple transmitters, these used to be based on a Wheatstone bridge and a standard cell with Cold Junction Compensation but I'm surely way out of date.

Ice or boiling water as a quick and dirty check.

RE: How to perform temperature sensor calibration at site ?

I've used ice bath and boiling water (need to know altitude/pressure for the boiling water point). For NIST traceable need a calibrated thermocouple as reference and also a calibrator like a FLUKE 726 so you get the reference TC hot along with your target (in a dry block/furnace sand) and then check both output to see if it is still in spec. They also have small sand fluid bed's with heaters etc. http://www.omega.com/pptst/FSB.html

RE: How to perform temperature sensor calibration at site ?

I can see using a fluidized bed to calibrate a number of instruments in a fixed location but you would hardly lug it up the side of a column to check an instrument in a Hazardous location

You assume your Platinum wire RTD is accurate, if not don't fudge the transmitter to make up for it.
Substitute a precision decade box and set the transmitter to give the correct output.
You cannot always get access to the temperature element for example the 10 Ohm Copper or thermistors in a motor but the Decade box is universal.

Sometimes you encounter American Curve .00392 when expecting European curve .00385 RTDs, I can see a fluidized bed being useful for that but boiling water will do just as well to identify the type.

Thermocouples don't drift either, use hot water and a thermometer to prove it's working but a calibrator for setting the transmitter.

RE: How to perform temperature sensor calibration at site ?

For RTD use decade box and set your resistance according to temperature.Fotr thermocouple use mv source .

RE: How to perform temperature sensor calibration at site ?

We use an Omega CL355A and send it out to be calibrated to maintain the calibration chain

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close