Frequency of Measuring Pipe Expansion Ratio
I was wondering how often does API 5L require calculation of the sizing ratio? Is calculation of the sizing ratio the only requirement to verify the expansion? Since the sizing ratio is determined by taking measurements on the outer diameter, do the same rules apply for validation of expansion and determining the sizing ratio? Or does the sizing ratio need to be checked more often then the OD?
I would appreciate any insight or resources that could be pointed to as a useful reference.
below are some quotes from API 5L
8.2 Processes requiring validation
Final operations performed during pipe manufacturing that affect attribute compliance as required in this
Standard (except chemical composition and dimensions) shall have their processes validated.
Those processes requiring validation are the following: for SAW and COW pipe, expanded: pipe forming, seam welding, repair welding, expansion
10.2.8.1 The diameter of pipes shall be measured at least once per 4 hours per operating shift to verify conformance to the diameter tolerances (see Table 10).
Table 18 — Inspection frequency for PSL 2 pipe (continued)
Test Type: Pipe diameter and out-of-roundness for pipe with D ≤ 168,3 mm (6.625 in) SMLS, HFW, or SAW
Frequency: Once per test unit of not more than 100 lengths of pipe
RE: Frequency of Measuring Pipe Expansion Ratio
