Distribution transformer 2000KVA,11000V/433V
Primary current=104.97A
Secondary current=2666.82A
So the CT ratio for the load side energy meter will be 3000/1A
but i need to calculate from the below cause
Output load around 1600KW/If the load 1200KW what will be the energy meter CT ratio selection
Primary current=104.97A
Secondary current=2666.82A
So the CT ratio for the load side energy meter will be 3000/1A
but i need to calculate from the below cause
Output load around 1600KW/If the load 1200KW what will be the energy meter CT ratio selection






RE: Distribution transformer 2000KV Ou
RE: Distribution transformer 2000KV Ou
Schneider Electric Cahier technique no. 194 current transformers
https://www.ops-ecat.schneider-electric.com/cut.Ca...