(OP)
Distribution transformer 2000KVA,11000V/433V

Primary current=104.97A
Secondary current=2666.82A

So the CT ratio for the load side energy meter will be 3000/1A

but i need to calculate from the below cause
Output load around 1600KW/If the load 1200KW what will be the energy meter CT ratio selection

RE: Distribution transformer 2000KV Ou

Same, you need to size the CT on maximum load so that it can accommodate the distribution transformer loading.