POst/column load on a slab near a free edge.
I've looked at point loads and walls at/near a free edge, but now I have a client who wants to build a small Ramada on an existing slab. The max load is small (<4000#'s)and I've checked punch and uplift/pull out, but with Ringo and Anderson's procedure I'm getting irregular results. The column placement is right at 1 X the relative stiffness - 1.5 is preferred, but I should get some result to quantify my results.
FYI, we have no frost, so depth is not an issue, I'm taking k as 100-pci and f'c at 2500. my gut tells me I'm OK, but I'd like some backup.
TIA,
fadams
RE: POst/column load on a slab near a free edge.
Can you up the concrete strength a tad and 'throw a couple of top bars in?
Dik
thanks Dik, but slab is already in. Trying to avoid saw-cutting a perfectly good slab for a 4K load.
f
Do you have the budget/time for a FEA model? With 100 pci subgrade and only 4k load, I would think just about any slab would be ok. (If the load is properly distributed.)
How thick is the slab?
WARose, slab is 5" and I don't have software for FEA unless there's a way to trick RISA.
f
If you've got RISA......you've got FEA. RISA (at least the last time I used it, which has been years) allowed you to model plates sitting on springs.
What is your contact area (on the surface of the slab) for the 4k load? I can run it myself in a spread sheet I have.
I ran it myself (based on the sketch) with a few software packages I have and I came up with the slab being light as well. (I was visualizing a thicker slab before.) You may have to cut out the slab at those locations and put in footings.
OK - will proceed accordingly. Thanks again WARrose
WARose - you still have RISA to look at a model??
No. I have STAAD Pro. You could probably still post a pic if you want.