AC Drive tripping motor protection switch heat problem
AC Drive tripping motor protection switch heat problem
(OP)
Hello!
we have here one AC drive (ABB ACS800) that has four (4) motor in parallel. The drive is 16amps and the motors are 0,75kw 1amp 690V each.
each output from the drive to the motor has an individual motor protection switch, sized to 1,6Amps
the thing is that te motor protection switch are heating too much today I measure voltage drop and I have 1 volt drop and 1 amp current in each phase.
please see attached pictures.
does anyone have any hint?? is that drive output to four motor in parallel has too much high freq component that causes overheat and problems with bimetallic mechanism??
the cables are 2mm and they are not overheated, also it has a contactor and not overheated, only the motor protection switch!!! I measure ac current rms and I measure 1 amp in each phase for all motors (all motors are the same)
any hint???
we have here one AC drive (ABB ACS800) that has four (4) motor in parallel. The drive is 16amps and the motors are 0,75kw 1amp 690V each.
each output from the drive to the motor has an individual motor protection switch, sized to 1,6Amps
the thing is that te motor protection switch are heating too much today I measure voltage drop and I have 1 volt drop and 1 amp current in each phase.
please see attached pictures.
does anyone have any hint?? is that drive output to four motor in parallel has too much high freq component that causes overheat and problems with bimetallic mechanism??
the cables are 2mm and they are not overheated, also it has a contactor and not overheated, only the motor protection switch!!! I measure ac current rms and I measure 1 amp in each phase for all motors (all motors are the same)
any hint???





RE: AC Drive tripping motor protection switch heat problem
Yes you could be having heating from the carrier frequency. Have you tried turning down the carrier frequency to see if it alleviates the issue?
I doubt your meter is also giving you the correct info due to the same modulation frequency. A total of 3 measly watts spread over three contacts seems too low to be baking things as your pictures show. It may well be more losses than you're measuring.
Keith Cress
kcress - http://www.flaminsystems.com
RE: AC Drive tripping motor protection switch heat problem
I suggest re-terminating the cables using a good-quality crimp lug with a flat blade or forked end, such as those made by Cembre or Elpress, and which are typically coloured blue for 2.5mm² cable. For example, http://www.cablejoints.co.uk/sub-product-details/c...
RE: AC Drive tripping motor protection switch heat problem
B) Without even looking for and reading the manual for them, I'm going to go out on a limb and say that the installer (don't know if it is you or if you inherited this) did not follow the manufacturer's instructions regarding spacing and "heat stacking"; the problem of heat from one unit rising into the next, then the next, etc.. Most devices like that require at least 1" (25mm) of spacing, and even then if it is being used on a VFD circuit, I would not push the envelope, give any current carrying components plenty of room to "breathe". So so many times I see people try to cram way too much electrical equipment into spaces not suited for them, then complain about parts over heating.
Electricity flow = heat...
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: AC Drive tripping motor protection switch heat problem
Keith Cress
kcress - http://www.flaminsystems.com
RE: AC Drive tripping motor protection switch heat problem
If heat stacking is an issue the upper devices may be more prone to tripping.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: AC Drive tripping motor protection switch heat problem
this MCC came as shown from factory but even though distance is short there must be something else.
I measured with an AC clamp true rms, 0,9-1,1 amps and I regard this as very low current to overheat the motor protection switches. The heat is true, you can't hold your finger on it. Someone changed one to 4amps and the heat is less, but still some.
the drive has no output filter, this I regard as a problem. Can the heating element inside the mot. prot. switch be affected by other frequencies than 50/60hz that I cannot measure with a true rms clamp?
best regards,
martin.
RE: AC Drive tripping motor protection switch heat problem
https://cache.industry.siemens.com/dl/files/798/24...
RE: AC Drive tripping motor protection switch heat problem
RE: AC Drive tripping motor protection switch heat problem
RE: AC Drive tripping motor protection switch heat problem
Keith Cress
kcress - http://www.flaminsystems.com
RE: AC Drive tripping motor protection switch heat problem
This I don't regard as big problem BUT they want to put 5 (five!!!) 15kW motors in parallel... so I was around this issue mainly because they want to do the same application but larger power in a couple of months!!
I didn't know of this problem but electricians have been changing motor protection switches for a while...
While looking at this and thinking on the same problem in larger power application... BIGGER PROBLEMS?!?!?!
Im thinking in advice for SINE output filter and electronic current measurement (using CT's)
Also DCS logic to power ON/OFF motors they are making WITHOUT stopping the drive!! Now operators can stop one motor without stopping all four. They reported once replaced the drive because of a fault but I think control logic must stop drive then exclude motor and start again!!
kind regards,
martin
RE: AC Drive tripping motor protection switch heat problem
regs,
martin.
RE: AC Drive tripping motor protection switch heat problem
You might be able to get away with stopping a drive while the VFD is running, but starting a motor on a running VFD is a bad thing to attempt.
RE: AC Drive tripping motor protection switch heat problem
Keith Cress
kcress - http://www.flaminsystems.com
RE: AC Drive tripping motor protection switch heat problem
https://library.e.abb.com/public/fd98d8fd5ca4492cb...
I would review rules in this PDF that the manufacturer put out and see if that is the case.
Above the advice was to look at the freq that is put out by the drive. There is a particular rule that ABB put out that should be followed.
Para 2606 Effective switching freq = 4khz minimum
Other freq to start of 2khz should not be used.
Volts/hz setting was also stated as one of rules to follow.
Question: Does the drive disable when one of the motor protectors are tripped? I would think you would want to disable the drive if one of the motor protectors tripped.
RE: AC Drive tripping motor protection switch heat problem
thanks to all
kind regads,
martin
RE: AC Drive tripping motor protection switch heat problem
https://library.e.abb.com/public/f09dd2f0e92e45f28...
The right hand doesn't talk to the left hand I guess...
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: AC Drive tripping motor protection switch heat problem
Quote-----------------
Challenges with use of standard MPCB at output of VFD
Reflections of the voltage pulses
Occur at the terminals of the motor due to the PWM voltage pulses and the surge impedance of the motor. Amplitude is dependent on:
System voltage
Voltage rise time trise of the VFD
Current rating of the MPCB (surge impedance)
Operational voltage (DCBUS-voltage)
Location of the MPCB (close to the VFD output or close to the motor)
Cable type and length between MPCB and motor (surge impedance)
MPCB rated < 10 A are more susceptible to voltage wave reflections (higher surge impedance)
Reflected voltage pulses cause high dielectric stress on the MPCB magnetic trip coils resulting in accelerated aging
Unquote----------------
then talk to a particular part number below
Quote----------------- I do not think both ABB ever talked to a particular part number?
AB 140M-D8V are suitable for application at output of VFDs in multi-motor installation
PWM frequency ≤ 4kHz
VFD output frequency ≤ 400Hz
Current setting = rated motor current
Maximum cable length of drive instruction manual apply
Preferred location of MPCB installations is as close to the motor as possible
Unquote----------------
The ABB pdf is showing <8khz PWM freq
RE: AC Drive tripping motor protection switch heat problem
If they wish to replicate this system with 15kW motors, and be able to start-stop with the contactors (ie not with the drive), what size of drive are you considering?
Currently the drive is 16amps and the motors are 0,75kw 1amp 690V each, and you are having issues. To extrapolate up to 15kW motors, you would require a 320A drive. Of course you won't go to this extreme (mostly because of cost). Obviously in this extreme example four (4) 20A drives would likely cost less then (1) 320A drive.
I would think that you would not wish to be less than 160A. This could accomodate inrush current (ie 7X IFL) + 3 remaining motors running at full-load.
GG
ps What is the nature of the load (ie constant or variable torque), speed range.
"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)
RE: AC Drive tripping motor protection switch heat problem
One of the advantages of a VFD versus DOL starting is is the ability to ramp up the speed.
With an oversized VFD you may be able to do it.
On the other hand the VFD may not like the starting surge even if it is within the nominal capability of the drive.
Please let us know how this works out.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: AC Drive tripping motor protection switch heat problem
acs800 - 120A - 690V with dU/dT filter (not sine)
15kW motors 690V x 5
application: FAN
5 motors in parallel, each with it's corresponding mot protection switch and contactor.
well I was taking a look at the application, and suggested to remove output motor selection, i mean removing output contactors and not make any logic of it, there's not real need for operation to switch on and off the Fans.
Also, Motor protection switches shall shutdown the drive permanently (for.ex. put a contact in series to external fault digital input of the drive) because I think there's a risk of an electrician to switch on (by hand) the mot protection switch while the drive is in operation, I guess there's an important risk for drive and person. Also if you want to run with four motors, electrical people have to disconnect the motor and jump the Mot.prot. switch contact, I mean they will need to go through the risk inolved and circuit and think about everything.
As for the 1amp motors of the beginning, there will be a modification of the switching on and off the motors, that will include switching off and on the drive before acting on the contactors. I suggested a sine filter but that's ongoing yet.
But let's see how's this beast runs! they need to install everything yet I guess couple of months to the commissioning but I promise to report back how this works
(I won't be involved in the commissioning... ...yet...)
thanks to all,
martin
RE: AC Drive tripping motor protection switch heat problem
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: AC Drive tripping motor protection switch heat problem
And function
bypass on(motorN) + motor protector tripped or turned off(motorN) +next motor = enable to drive
or
bypass off motorN) + motor protector on or turned on motorN) +next motor = enable to drive
RE: AC Drive tripping motor protection switch heat problem
Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
RE: AC Drive tripping motor protection switch heat problem
RE: AC Drive tripping motor protection switch heat problem
Simplify Your Application: Control Multiple Motors with One VFD
http://www.rockwellautomation.com/en_NA/training-e...