Extending existing circular concrete water tank
Extending existing circular concrete water tank
(OP)
I have a client who wants to add an additional 8' in height to their existing water tank. The existing tank has an inside diameter of 22' with 12" thick walls and has a depth of 10'-6". I have not seen the tank empty so I do not know what the conditions are at the bottom or what kind of footing it has, but it felt like a concrete slab when I hit it with the tape measure. The existing reinforcement is unknown so we are having it scanned so we can determine if the reinforcement is adequate for the additional water pressure. My question is how to extend the tank wall up. My initial thought was to dowel into the top of the existing wall and build up on top of it and have a waterproof joint in between the two (Option 1). The builder also mentioned possibly coming around the outside of the wall with the extension (Option 2), which I am thinking might be a better way to go, although I'm not sure exactly how to waterproof that joint. I attached a sketch showing both options. Also, any tips on waterproofing the joint would be greatly appreciated.






RE: Extending existing circular concrete water tank
Get a copy of the PCA pamphlet "Circular Concrete Tanks without Pretressing" to help your analysis. It's the best 45 dollars you'll ever spend.
RE: Extending existing circular concrete water tank
"Circular Concrete Tanks Without Prestressing", c. 1943, PCA, 32 Pages
www.SlideRuleEra.net
www.VacuumTubeEra.net
RE: Extending existing circular concrete water tank
RE: Extending existing circular concrete water tank
www.SlideRuleEra.net
www.VacuumTubeEra.net
RE: Extending existing circular concrete water tank
RE: Extending existing circular concrete water tank
If the existing wall reinforcement is not adequate to resist the additional water pressure, perhaps it could be reinforced with prestressed strands wrapped around the exterior and protected with a pneumatically placed concrete cover.
BA
RE: Extending existing circular concrete water tank
Jed, thanks for the Sika link, I usually spec the swelllstop but did not realize they had a post install product.
As far as the additional load on the soil, the total water pressure at the bottom is about 1200 PDF which isn't too bad, but we don't have a soils report. I'm more worried about the additional wall weight as BA mentioned, which will total to about 2800 plf at the base of the existing wall. I guess we might need to have them excavate at the exterior of the wall to see what's going on with the footing down there. We will probably need to approximate a conservative bearing capacity and see if it can handle the additional load.
One mor question. For option 1 would you think the tank needs to be analyzed as a monolithic structure and the dowels sized to transfer moment and shear? I know on paper it seems like a stable structure assuming a pinned base between the two, but I'm a little afraid of separation between the two developing and compromising the water tightness. On the other hand, it would obviously be preferable from a construction stand point to keep the dowel spacing and embedment to a minimum, either staggered on each face as Jed mentioned or down the center
RE: Extending existing circular concrete water tank
In addition, I'm a believer is a belt and suspenders approach, especially when you have significant unknown conditions.