Wide rc beam on small column

Wide rc beam on small column

Wide rc beam on small column

(OP)
Hi

Recently i design a wide rc beam 2.4m x 0.6m with supporting one way rc slab.  Should i use the normal design method of RC beam with ratio of width /height <1.0 to design wide beam ?  how does the load at the overhang of beam near the small column transfer to the column if we use normal conventional method of designing the wide beams supported on small column.  Any suggestions ? Thanks

AL  

RE: Wide rc beam on small column

Typically, one way shear is critical on r/c beams.  In your case, punching shear is more likely to govern.  I would also check a short portion of the beam bending in the 2.4 meter direction over the top of the column.  What you are designing is somewhat similar to two way slab construction, in the way load enters the column.

DaveAtkins

RE: Wide rc beam on small column

(OP)
Thanks for the tips, Daveatkins.  
Refer to the same topic, how long is the short portion of beam bending in the 2.4 meter direction over the top of column need to be used for checking.  Would the wide beam subject to torsion  when one side of one way slab is loaded with live load ?  

RE: Wide rc beam on small column

I'll answer your second question first.  The large beam and the two adjacent slab spans will share any torsion according to their relative stiffnesses (the torsional stiffness of the beam and the flexural stiffnesses of the two slab spans).  The answer to your first question is:  use engineering judgment.  Certainly using only the width of the column is conservative.  But perhaps using the width of the columns plus twice the effective depth of the beam is reasonable, as well.

DaveAtkins

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources