we are facing problem at site for achieving the below shell DEP requirement for the tank foundations sand compaction
The first sand layer shall be compacted with a
plate vibrator to achieve a minimum strength or density of 5 MPa or 98 % Proctor.
The thickness of the compacted layer shall not exceed 0.3 m. The sand shall be
placed and compacted at Optimum Moisture Content ± 2 %.
note the sand saving show 99% less than 5 mm passing
if any recommendation how to achieve this value please help
regards
we are facing problem at site for achieving the below shell DEP requirement for the tank foundations sand compaction
The first sand layer shall be compacted with a
plate vibrator to achieve a minimum strength or density of 5 MPa or 98 % Proctor.
The thickness of the compacted layer shall not exceed 0.3 m. The sand shall be
placed and compacted at Optimum Moisture Content ± 2 %.
note the sand saving show 99% less than 5 mm passing
if any recommendation how to achieve this value please help
regards





RE: good morning we are facing prob
A lift thickness of 0.3m is too thick to be compacted properly with a small plate compactor. Forget the 5MPa requirement and compact to 98% of the Proctor. That's easily tested.
The key to getting compaction will be controlling the moisture content. Keep it as close to optimum as possible.