Lock Washer at Open Web Steel Joist Bolted-Connection
If the final connection for an Open Web Steel Joist (OWSJ), to support, were to be a bolted-connection, would a lock-washer provide any credible structural integrity?
Thank you!
RE: Lock Washer at Open Web Steel Joist Bolted-Connection
Most lock washers do nothing but make people feel good.
https://www.youtube.com/watch?v=IKwWu2w1gGk
Nord-Locks and Loktite are the only ways I trust to work the majority of times with minimal QA/QC. Cotter-pins and wiring the bolts are good but rely on installers to install it properly and a lack of QA/QC can hurt them.
Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries
https://www.facebook.com/AmericanConcrete/
Additionally, the RCSC has no test data for connections using lock-type washers, so they are not pre-qualified for use in bolted structural connections. I advise you stick with the connection details for which there are published, test-validated load capacities.
Dave
Thaidavid
No.
NASA's Fastner Design publication, 1228, states lockwashers are useless. The Navy's Ship Manual (S9086-CJ-STM-010/CH-075R2)Chapter 75 prefers locking nuts; although it states that lockwashers can be used on diesel equipment if there wasn't any previous bolt loosening.
I propose we re-label "lock washers" as "slip washers" so clients and equipment vendors stop asking for them. Double talk should not be tolerated in engineering.
If properly 'snug tight' should not loosen.
Dik