Due to site condition the original arrangement of bars in concrete beam of one layer of 10T32 has been rearranged to 2 layers of 5T32. Is there a big impact in section capacity of the beam?






RE: Camparison of section capacity of concrete beam of rearrangement bars in beam
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: Camparison of section capacity of concrete beam of rearrangement bars in beam
----
The name is a long story -- just call me Lo.
RE: Camparison of section capacity of concrete beam of rearrangement bars in beam
- I'm guessing this raises your reinforcement centroid about 1.5" (32 mm x (0.5 + 0.7)). Thus reducing your effective depth 1.5".
- For this change to affect your capacity by more than 5%, you're beam would need to be shallower than 30".
So, in KootK-land, we'd be letting this roll if the beam was 30" deep or more.