When a landlord uses a 'butcher' not a welder to modify a PEMB column
2

When a landlord uses a 'butcher' not a welder to modify a PEMB column

When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
A landlord owns several large warehouses in my area, with long-term tenants. The landlord keeps the buildings in good shape, and is proactive in upgrading and maintaining the roofs, wall envelope etc.

He recently upgraded the roof drainage system, providing new 6" Ø PVC pipes to remove roof gutter water, and routed the vertical pipes through the warehouse and then laterally through the two perimeter internal PEMB tapered steel columns.

For some reason (money I assume) he hired the local 'butcher' and not the local experienced fabricator, who proceeded to use a 5" grinder to cut a 8.5" ø hole in the web of the column, so as to install a pipe-segment reinforcement which was to be welded to the web after installation.

The hack-job resulted in gaps of 1"+ around the scribed 'cut', as follows:






A welder he is NOT!


RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I like how the original marked hole location wasn't even correct.

Oh well, if there's not enough time to do it right the first time there's always more than enough time to do it right the second.

Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries
https://www.facebook.com/AmericanConcrete/

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Hiring the butcher was the second mistake. Giving priority to the drain pipe over the building column was the first.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

My Eyes!..... They Bleed
i'm surprised they considered sleeving the penetration and drain at all.
This makes me think about how there really should be an open thread where people post their most FUBAR construction photos on this site. i might get one going but there are so many good choices.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

At least they didn't try to run it through the flange!

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I would tend to believe that the quality of the hole is irrelevant. The fact that you have a hole that large in a column that was probably designed to within 99.99% of the allowable stress is the bigger issue. In other words, even if the hole was made with surgeon like precision, the column probably no longer works.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Ingenuity, do you know any of the back story? Were you the designer, or know whether this was designed by an engineer?

A couple of previous posts suggest that a pipe penetrating the web is a no-no but that will depend on the circumstances.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Who did the engineering?

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Quote (MotorCity)

I would tend to believe that the quality of the hole is irrelevant. The fact that you have a hole that large in a column that was probably designed to within 99.99% of the allowable stress is the bigger issue. In other words, even if the hole was made with surgeon like precision, the column probably no longer works.

99.99% would make them one of the more conservative PEMB engineers. I've heard 103% is pretty standard.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Hey: Feel sorry for the poor guy. That's the best you are going to get out of a $100 flux core welder that, under the best circumstances with 1/16" metal, will look only a little better. Some might term the result "good enuff". The cutting torch rig that cut the hole cudda done better, but golly the welding tips got lost.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

6 inch PVC pipe, looks like it is inside an 8" "pipe" (not structural steel!) not-really-welded into an irregular (stress-riser!!!) 10 in dia irregular hole burnt into the web of a thin-walled light PEMB column with a 14 inch web. The 8 inch dia "pipe" might help as a guide to prevent the PVC from being cut as it flexs and bends, but the fact that the PEMB "structural column" is now acting as a pipe support/pipe restraint increases the load axial to the pipe centerline.

No, that column has no strength left, no vibration or fatigue resistance. And now an increased irregular load.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Can you advise him of your concern and have him get it properly engineered? As it stands, the building is compromised.

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I think it's ridiculous to say the column has no capacity. If this has been properly engineered, the easy fix is to cut out a bigger hole, full-pen weld in new plate, and properly cut a new hole into the column. If not, all the above minus putting in a new hole, and relocate the drain pipe.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)

Quote (hokie66)

Hiring the butcher was the second mistake. Giving priority to the drain pipe over the building column was the first.

hohie66 - ain't that the truth.

Backstory: PEMB designed and constructed in mid 80's. I am not involved with the original nor current engineering/design of this building or repair, however, a PE who is a friend of mine is a friend of the building owner. You see where this is going! Building owner says to PE that he HAS to re-route the piping and CANNOT loose any net lease space so wishes to cut a SMALL hole in the column web. I believe the PE did a sketch or two of the proposed hole size and reinforcement, and expected that a competent fabricator/welder would undertake the work. Fast forward to where we are today - I get a call from PE to see if I can "take a look at the column" because I am pretty handy with a welder - I go take a look and see this monster! I was expecting a neat field flame-cut edge, with a weld that I may have to 'resurrect'...walking away, shaking my head...

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

OK, so I'll give the engineer the benefit of the doubt. You say it's a warehouse so perhaps this is actually a bending member primarily and the loss of web is unimportant. Even if it's a compression member, it may be governed by buckling in which case the web is again relatively unimportant. After all, it's still got more steel than a truss or a castellated beam.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)

Quote (steveh49)

You say it's a warehouse so perhaps this is actually a bending member primarily

A typical US tapered steel column in a frame, light vertical loading, CMU/block perimeter walls - like a "portal frame" in AU, but in the US the design is done by the PEMB (pre-engineered metal building) company and they often use built-up members and seldom use UB/WF haunches at column/rafter connections, like is done in AU.

Maybe a market for cellular/castellated column sections to accommodate building owners and their 'butchers' smile

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

If it is in a low moment area of the column, the intended repair would have probably been fine. It is just the workmanship which has ruined it. Like canwesteng said, they need to get a competent tradesman to cut this all out and do it properly.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Just leave it.... it will make good reading in the 'Engineering Failures and Disasters' Forum

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Get a larger steel cover plate fabricated with the proper diameter and weld it in. Estimate the shear in the beam/column and see if it is significant.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Ok, i do not condone what was done in any way and I understand that metal building members are designed to 100% of their capacity but I have to wonder about a few things. Usually a web is designed for shear, and this hole is in a tapered column. If the column is 12" at the base and 24" where the hole was cut and the web is the same thickness how bad is the situation?

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I think the only repair is to remove the pipe section and grind the one side flat and to weld a new plate over the existing hole. The plate to the flange with a fillet weld and the hole area to the plate also with a fillet weld. the hole can then be cut using a circular hole saw drill and then weld a new pipe in place. The fabrication should be designed so that the strength of the PEMB member is not compromised.

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
Follow-up: I got to visit the project up-close last week, and was able to determine that the web thickness is 5/32" (4mm), flanges are 1/4" thick x 6" wide. Interesting that the web/flange weld is continuous to one side only - no weld whatsoever to opposite face - is this typical for web-tapered/fabricated members for PEMB's, assuming small magnitude of loads/actions?

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Quite common weld since they don't have to 'flip' the assembly to weld the other side and it can be set up automatically.

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Really? That seem like a flange stability nightmare. Any tendency for the flange to rotate would put the welds in pure bending w/o any other alternatives.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

If the web is only 5/32, the web itself just past the weld isn't much better (even if you were to weld both sides).

Granted, you theoretically have a "crack" starting right at the root of the weld, but maybe practically you end up with enough incidental weld penetration to mitigate that.

----
The name is a long story -- just call me Lo.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Poor man's partial pen?

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
dik: Yes, I think you are correct.

KootK: Yes, bending about the long't axis of the weld was my concern.

Lo: I guess when you only have 5/32" of thickness to work with.

Just looks 'off-putting' - but not as 'off' as the web hole smile





RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Koot

The single sided welding issue is addressed in Newman's "Metal Building Systems Design and Specification" in the section "Some Contention Issues of Design and Fabrication."

The general thrust seems to be that some people don't like it, but testing seems to show that it's generally okay with an exception of a specific seismic case.

"According to a test program performed by Prof. Thomas M. Murray, single sided welds do not reduce the ultimate structural capacity of the primary frames, except in the end-plate connections where seismic loading is involved. The simulation of cyclic seismic forces in the test program produced repeated local buckling, which resulted in fracture of the single sided welds in the frame rafters near the end plates. Some feel that single sided welding may be acceptable for static loads but not for frames subjected to lateral forces, concentrated loading or fatigue, where double sided welds should be used. Naturally, most rigid frames must resist both gravity and lateral loads."

Since the description of the item that was seeing failure is confusing, I chased the references. See this letter from Dr. Murray, which gives more context (first letter on the page):

https://www.aisc.org/globalassets/modern-steel/arc...

His letter is in response to this article,

https://www.aisc.org/globalassets/modern-steel/arc...

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
TLHS: Nice research work. I shall read those references. Thanks.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

TLHS: I'm going to disagree slightly here about the single sided welds. There isn't a lot of code literature (or research) that penalizes them right now. But, there have been some efforts (related to single sided welds for HSS connections) which show that these welds do not exhibit regular increase in strength when they're put into tension. REference the AISC design guide on HSS connections.

They're beginning to realize that this may not just be an issue for HSS shapes, it's just that not many people have really tested them outside of HSS connections. Not saying that I know what's going to come of all this. I just want to add a caveat about this type of weld and why "some people don't like them" as you say. The theory (as KootK suggests) is that bending / torque about the long axis of the weld may be a problem when the connection is in tension.

Now, this connection one-sided connection weld may not be bad because it may be pure shear. So, I'm not wholly disagreeing with your comments. Just offering some caution about this type of weld.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I don't know that I'd trust testing to show that the single side weld is okay - your fusion face is well past the joint depending on the quality put into the weldment, so you are getting some degree of PJP here. I can see that working ok in testing, but I wouldn't want to rely on it in practice since it's hard to quantify and technically a better welder will do the weld faster and leave less fusion into the joint.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)

Quote (TLHS)

The single sided welding issue is addressed in Newman's "Metal Building Systems Design and Specification" in the section "Some Contention Issues of Design and Fabrication."

I have Newman's 1997 edition and could not find this section - what edition is this in, TLHS?

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Most PEMB web/flange welds are done as a submerged arc process (semi-automatic weld equipment). This results in a fillet weld that has relatively deep penetration into the web effecting as noted above a somewhat PJP weld. Years ago AISC actually allowed a reduction of 1/16" of actual weld throat for such a weld to recognize the penetration. That allowance has now been removed, although specific testing in regard to sectioning samples produced by the weld procedure could allow someone to take the penetration into account. Dr. Joe Yura at U. Texas has tested both small PEMB beams as well as some bridge box girders that utilized single sided welds and found no issues with their use. The one area where we mandate a double sided weld would be for a 3-plate fabricated crane beam assembly due to the fatigue issues. The fabricated crane beam is a rarity unless requiring such for a long span beam (40-50') in a special situation.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Josh,

The discussion was, as I understood, about flange to web welds. I would agree that welds that see significant tension should be on both sides. So, barring research to the contrary, if there's a point tension load on the lower flange, I would expect that the eccentricity of the weld would result in a strength loss from the resulting moment. For example, I'd never weld a shear plate on the column side on just one side.

Personally, I also wouldn't weld a web to a flange on just one side, but I have trouble calling it bad practice.

Ingenuity,

My copy is the second edition (2003), so perhaps yours doesn't include it? In mine, it's at the end of Chapter 16 "Avoiding Construction Problems"

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I think it's bad practice to count on the fusion zone to extend pass the heel of the fillet, and I think without it the single weld wouldn't do so well in testing.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

A few comments:

Welding from one side for thin material is not unsafe. The weld is substantially subjected to shear and the distances are usually far enough apart to resist any flexural moment issue. For thicker web members, the issue becomes a little more murky.

There is economy in only welding from one side, albeit small, but if you manufacture a kazillion of them, the savings adds up.

Unless I have tension issues, I detail base plates so that the fillet weld can be made without 'flipping' the column; the fillet weld is on one side only. Again, a small savings, but, a savings nonetheless.

In the second paper, there was a discussion about how a fabricator can be more competitive with PEMB's... I don't think it's possible since a PEMB manufacturer designs everything to the limit for cost effectiveness. If a fabricator were to take the same approach he would become a PEMB manufacturer and no longer a fabricator.

I think of PEMB's as 'throwaway' buildings, and after 25 or so years are good for scrap (I know there are a lot older). They have limited use except for an initial enclosure. I work with a lot of industrial buildings, and it is not easy to modify them or analyse them. I generally advise the client to stay away from them.

Dik



RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

@TLHS: thanks indeed for the information and for taking the time to educate me/us on this topic. It's reminiscent of a recent thread dealing with insufficient welding in the built up beams of a special moment frame. There, seismic steel codes specify -- and research supports -- that full penetration welding is required adjacent to the moment connections but is not required elsewhere along the span. Kinda seems like the amped up, inelastic rendition of this same concept. I do like it when stuff ties together.

While Murray's research findings are very convincing, one of Nawrocki's salient points was that of the flanges getting knocked away altogether under forklift impact. That still strikes me as a valid criticism. That said, perhaps once you're down to to a 5/16" web and a 1/4" flange, you've got that same problem regardless of how you prosecute the welding.

While I've been somewhat skeptical of this particular PEMB practice here as a result of my own ignorance, I should clarify that I hold the PEMB industry, and it's more skilled practitioners, in high regard. As with any field, the worst of them are terrible. But the best of them are pretty much steel design maestros in my experience. And their product generally does a great job of meeting the requirements of the clients, irrespective of the ire of the renovators that sometimes come later.

@Ingenuity: for your viewing pleasure... It is from the second edition should you be interested in acquiring a copy.


I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)

Quote (TLHS)

My copy is the second edition (2003), so perhaps yours doesn't include it? In mine, it's at the end of Chapter 16 C

Thanks. My 1997 Edition has the chapter "Avoiding Construction Problems" but no reference to single-sided welding.

Quote (KootK)

@Ingenuity: for your viewing pleasure... It is from the second edition should you be interested in acquiring a copy.

Thanks. I notice there is now a 3rd Edition. Added to my wish-list.

Quote (KootK)

perhaps once you're down to to a 5/16" web

I wish it was 5/16"...this one is only 5/32"!


Quote (Jeffrey S. Nawrocki, P.E. 'HOW FABRICATORS CAN COMBAT METAL BUILDINGS':)




A Cat 980 loader is a 'beast' in the hands of an operator.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I suppose it would be odd to have a flange thinner than the web.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

KootK... high shear? <G>

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Flanges thinner than the web create issues with differential cooling of the flange/web weld. That can result in very wavy flanges. There are similar issues when a deeper section is used and web gets boosted for basic web/thickness ratio. This is particularly true when beam is deflection controlled so may have more depth than necessary for strength per se.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

For reference, a CAT 980 loader:



I've seen operators of similar loaders destroy everything and anything in a building. It's next to impossible to build an enclosed structure for those to operate in without having to rely on the operator's skill to not damage the structure. If they don't care if something is destroyed (or want to destroy it in the case of what I saw; a disgruntled worker) they will destroy it, hot rolled or not.

But, I agree with KootK's original point; I'd much rather see a double-sided weld with smaller equipment such as a forklift or similar (or armor the column). I'm sure everyone has seen a column flange all bent out of shape at a facility operating forklifts, I would imagine it wouldn't take much to rip off the flange on a single sided weld.

Professional Engineer (ME, NH, MA) Structural Engineer (IL)
American Concrete Industries
https://www.facebook.com/AmericanConcrete/

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Altho. I am not a structural engineer, to me, it seems that the job could have headed in the right direction but the execution was terrible and also perhaps a stress analysis lacking. A metal sleeve, of a proper thickness, could have been professionally welded to the hole cut thru the column web in order to reinforce the hole.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

In my mind, if you're worried about forklifts, loaders or heavy equipment, your best bet is to concrete encase or put up barriers within the areas you're worried about, rather than expecting that you can detail a steel column that won't get mangled.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

@TLHS: you're Vancouver based these days, right?

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I am indeed.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

TLHS... summer's coming... the rain is starting to warm up...

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
7/30/2017: ===> UPDATE:

I decided to drop by the subject warehouse on Friday and see how the repair of the 'hack-job' worked out. Not sure if the same 'butcher' returned to fix his/her handy work, or if the owner found another 'welder'.

Nothing like a coat of paint to cover over welds that look like "pigeon poo".

The welder must like using off-cuts from his/her shop floor - cause they sure used a bunch on this job.

FYI - the price of a 2' x 4' x 1/4" A36 plate (that would have been enough material to reinforce two webs (18" depth x 18" long at 2 hole locations) and on both faces) from one local steel merchant is $65! I know some of the welds are out-of-position but why on earth would you add all those tabs and off-cuts?

For reference, the existing tapered webs are 5/32" thick, and the flanges are 1/4" thick. The new 'profiled' web plates (I use that loosely 'cause the profile cut is not really 'profiled' nor straight) are about 5/16" thick.

Enjoy!

Photo 1: Looking up the web:


Photo 2: Looking face-on to web - note the tabs, and off-cuts:


Photo 3: More tabs and off-cuts:



RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
Oh, I near forgot - the new rainwater drainage pipes leak - there is significant water accumulating at the column bases:



It is a warehouse for school book storage, so water leaks are a big deal - besides the detrimental effect on the steel base plates and anchor rods.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I weld better than that, and, I'm not a welder...

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

I venture to say the "welder" hired for the repairs was hire based on his low quote, not his credentials. I would not categorize anyone that would perform a repair or deposits welds that look like those in the photographs as a welder.

I also understand the initial modifications were made without the involvement of an engineer. It would appear "price" was more important than "quality". There are lessons to be learned from this post.

The Owner and the engineer involved should verify the individual hired is qualified to perform the work in accordance to a drawing produced by an engineer. Let's face it, an competent engineer is needed to design and to provide a drawing or sketch of what must be done to maintain the integrity of the structural member and structure. I understand the owner is the party paying the bills and has a legal responsibility to ensure the structure is safe. The engineer has a responsibility to verify his design is properly executed. To that end, I would like to think the engineer would assist the owner to verify the individual hired to execute the repair was qualified to perform the work per the drawings. All little "ground work" up front can save everyone a lot of headaches later.

How much effort is required to request a copy of the welder's qualification papers and a copy of the WPS the welder would be using to execute the welds?

Whatever money was saved by hiring two "hacks" to execute the initial repair and the subsequent repair had to have been more than the cost of bring in a competent welder to begin with. The competent welder would have asked to see and would have followed drawings provided by an engineer. Few welders that understand the liability that is involved will simply forge ahead with a cutting torch in one hand and a electrode holder in the other without drawings to show what needs to be done.

Just my thoughts after reading the post and looking at the photographs.

Best regards - Al

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
gtaw:

You are absolutely correct in that "low quote" was the sole basis for selecting the repairs.

The PE (not original EoR) has known the owner for decades and knowing the 'cheapness' of the owner (and more importantly, the incompetence of his contractor) took it upon himself to get a cost estimate for the latest repairs using qualified and competent fabricators - the price was $3k total, for two column web hole repairs. When the PE presented the cost estimate to the owner, the owner freaked out (literally 'shouting and screaming') and said he will 'take care of it' - and the above photos depicts what "low quotes" get you.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

3k is kinda ridiculous for a repair of that type. Prolly a days work max.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)

Quote (XR250)

3k is kinda ridiculous for a repair of that type.

Maybe in NC, not in HI!

Access is not great - 36" of space behind vertical storage racking filled with books. If you are bigger than 6' or 200 lb you would not be able to access the two columns.

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

$3000 for the initial work would be on the high side, but not a repair of the butcher job completed by the first individual. I don't believe a $3000 price tag to repair the second butcher job would be out of the question. The repair of the repair isn't a simple task. A repair of a repair is at least twice, possibly three times as much work. Then again, you get what you pay for. This owner got exactly what he paid for.

Best regards - Al

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
gtaw:

Do you think these 'welds' were done using SMAW or FCAW process? I assumed it was SMAW and the 'user' had issues with electrode position and welding settings.

Thoughts?

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Most welders would be offended that the individual that facilitated this work is called a welder by anyone. This person can hardly be called anything other than a "hack".

It would be interesting to know whether the person even took the time to remove the paint in the areas to be welded or if a cutting torch was used to prepare the plates and whether the dross was removed from the cut edges before attempting to weld.

The type of steel used for prefab structures usually call for low hydrogen electrodes. I doubt the proper electrodes were used. Just because the electrode says E7018 on one end doesn't mean it is low hydrogen if it wasn't stored properly.

It is probably a good bet SMAW was used, especially if the work was performed in tight quarters. However, Home Depot and Loew's sell some pretty inexpensive GMAW/FCAW machines that make "anyone a welder". Just pull the trigger and poof - weld is deposited. At least that's what some people believe.

It looks like the work was done by an employee that owns a welding machine and sticks things together on the weekends. The "boss" probably had him come in over the weekend to perform the work for a little "extra overtime."

We'll never know the end of the story until there a good storm blowing and there is a news story of a partial collapse. With some luck, the building will stay intact and no one will get hurt. It is fortune the owner has a friend that took enough interest to look the work over and attempt to address the problem. There is just so much one can do when "stupid" people are involved. "You can lead a horse to water, but you can't make it wear a bikini."

One last comment; was the building department ever informed of this situation? There is a roll to be played by the building official when safety is involved.

Best regards - Al

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

Ingenuity:

among other issues... as I noted, I'm not a good welder, but a lot better than what was produced... looks like the guy went down to Canadian Tire (or the American Eq) and picked up a welder and decided to 'give it a try'.

Dik

RE: When a landlord uses a 'butcher' not a welder to modify a PEMB column

(OP)
gtaw:

Thank you for your detailed reply.

Quote (gtaw)

was the building department ever informed of this situation?

Pretty sure there was no permit from the city building department.

Quote (dik)

... looks like the guy went down to Canadian Tire (or the American Eq) and picked up a welder and decided to 'give it a try'.

I agree. Which ironically is what I did about 1 tear ago - purchased a $999 Lincoln 210 MP welder (FCAW/GMAW/SMAW processes) - but I restricted 'my learning' to an in-house 'ships ladder' to my warehouse mezzanine:



My welds were better looking than the 'hack' work of this thread - but I did learn some quick lessons on distortion with welding.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources