Is it IEC (CE) requirement to provide assisted start to 3 ph induction motor above certain size?

Is it IEC (CE) requirement to provide assisted start to 3 ph induction motor above certain size?

Is it IEC (CE) requirement to provide assisted start to 3 ph induction motor above certain size?

(OP)
Hello guy:
Does anyone know answer to question in subject line? If it is indeed requirement, can relevant documents to be sited? Motor in question is regular 3 phase squirrel cage induction motor. If this is just good practice in IEC world, then when (motor size) it needs to be used?

Best regards,

PaulBr

RE: Is it IEC (CE) requirement to provide assisted start to 3 ph induction motor above certain size?

On a sufficiently stiff system it's not unusual to have LV (400V) motors of 200kW - 250kW started direct-on-line. Motors this size require a large transformer of > 2000kVA to keep the voltage dip tolerable, and in my opinion motors greater than 200kW really should be on the MV system. I've heard of a few LV (690V) motors of 300kW+ being started DOL (with a suitably large transformer) but haven't actually seen one that large first hand.

There's nothing I'm aware of in the standards which mandates use of assisted starts for large motors, and any decision to do so which would come from sound engineering practice.

RE: Is it IEC (CE) requirement to provide assisted start to 3 ph induction motor above certain size?

By assisted starting I suppose you mean having a smaller motor used to accelerate the larger motor to some level before attempting to start the large one? Not that it matters because as ScottyUK says, there is no standard I am aware of requiring this, it's an engineering decision. Generally it's done when the mass is so large that the accelerating time at maximum torque will cause heating that will exceed the thermal damage curve of the motor. That is totally subjective.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: Is it IEC (CE) requirement to provide assisted start to 3 ph induction motor above certain size?

(OP)
I apologize for not being clear. I was using terminology that our customer was using. By assisted start they mean use of a) delta - wye contactor arrangement; b)soft start; or c)VFD. Motor in question is 3 phase, 50Hz,400VAC, 45kW motor. Customer is located not in EU but is trying to follow IEC standards.
We have searched internet and could not find any hints that such regulations exists. Only one paper was saying that if motor is class IE2 efficiency it needs to be using with VSD. Nothing was saying about "assisted start"

PaulBr.

RE: Is it IEC (CE) requirement to provide assisted start to 3 ph induction motor above certain size?

The power company would be the one who might have requirements on that.

RE: Is it IEC (CE) requirement to provide assisted start to 3 ph induction motor above certain size?

I agree with Lionel.
Many utilities limit the size of motors started DOL to minimize system voltage dips for other customers.

Bill
--------------------
"Why not the best?"
Jimmy Carter

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close