outdoor portable fire extinguishers installation

outdoor portable fire extinguishers installation

(OP)
shall the outdoor portable fire extinguishers installed in cabinet or not?

I appreciate Your cooperation..

RE: outdoor portable fire extinguishers installation

Normally not required

Unless the ahj requires it

Unless it is needed to keep it in its minimum and maximum temperature range established by manufacture.

A good idea to protect it from the elements.

RE: outdoor portable fire extinguishers installation

(OP)
thanks "cdafd", and shall be protected from the Sun rays or not??

I appreciate Your cooperation..

RE: outdoor portable fire extinguishers installation

Normally the cabinet would be used as a deterrent to vandalism. Breakable glass front would be the way to gain access to the cabinet.

RE: outdoor portable fire extinguishers installation

nfpa 10
Fire extinguishers installed under conditions where they are subject to physical damage (e.g., from impact, vibration, the environment) shall be protected against damage.

RE: outdoor portable fire extinguishers installation

nfpa 10
Fire extinguishers installed under conditions where they are subject to physical damage (e.g., from impact, vibration, the environment) shall be protected against damage.

Fire extinguishers shall not be exposed to temperatures outside the listed temperature range shown on the fire extinguisher label.

RE: outdoor portable fire extinguishers installation

In a hot climate, if the cabinet faces South, the temps can reach 150°F. That temp can solidify the ABC powder. Drilling holes in the cabinet can reduce the temp.

One of my competitors has changed from glass to plastic break-fronts. They paid an injury claim of $25,000.00 when a client broke the glass while removing the extinguisher.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close