Single Phase Arc Flash Label Requirements

Single Phase Arc Flash Label Requirements

Single Phase Arc Flash Label Requirements

(OP)
Based on the latest NFPA 70E and other latest references/guidelines are single phase panels in industrial facilities required to have arc flash labels?

RE: Single Phase Arc Flash Label Requirements

Depends on the incident energy, not whether it is single phase or not.


"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington

RE: Single Phase Arc Flash Label Requirements

(OP)
What do you mean based on the incident energy level?

Incident energy levels do not determine whether or not a specific device will get a label or not. If a device requires a label you would calculate the incident energy level to determine necessary PPE category, arc flash boundary, and etc.

My question is do these panels require labels, or is there some sort of exemption, as this will determine whether or not I will model them for inclusion in the study. I can not find anything stating clearly yes or no or even if a generic label would suffice but it is something that will play a large part of a project as the time to model and label these additional panels can become quite extensive in an industrial setting.

The 2012 edition stated an exemption for certain cases but the 2015 version does not in regards to label requirements it just list types of equipment in article 130.5(d).

RE: Single Phase Arc Flash Label Requirements

Quote (bcaine)


My question is do these panels require labels, or is there some sort of exemption, as this will determine whether or not I will model them for inclusion in the study. I can not find anything stating clearly yes or no or even if a generic label would suffice but it is something that will play a large part of a project as the time to model and label these additional panels can become quite extensive in an industrial setting.
All equipment or electrical control that would likely require examination, adjustment, service or maintenance while energized, creating the potential for an arc flash incident to occur--> should be labeled.
No ifs, no buts!

RE: Single Phase Arc Flash Label Requirements

I agree with trying to label all the equipment necessary for inspection. But the last I checked IEEE 1584 based their testing produced the formulas from a 3ph model. Sure we can use the formulas for 1ph calcs but this yields high results. I have heard in a seminar that their revamping the standard and the new IEEE 1584 will consider lower and single phase loads. I do know ETAP and SKM has some single phase arc flash modules but I don't think 1584 accounts for this so I'm not sure how ETAP and SKM does it or if the result they produce are conservative.

So should we label everything that needs inpection?... My opinion is yes but is there a standard in place that calculates single phase and lower voltages?

RE: Single Phase Arc Flash Label Requirements

(OP)
Exactly LionKing, thats a lot more data for a large plant which means more time and data, but... is it actually required or is there a standard.

ETAP gave the same reference to using IEEE 3 phase for conservative results and then tried to sell me on the single phase module but cant reference where single phase is actually required.

RE: Single Phase Arc Flash Label Requirements

NEC has required labeling on everything not in a dwelling since 2002.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources