very complicated installation case

very complicated installation case

(OP)
Dear members,
i have a problem that my company bought horizontal split case pump ( centrifugal type ) for a project , but the tank level is down by 3 meter the pump location as suction pipe goes horizontal for 2 meters and down for 3 meters.
the problem i need a reference from NFPA that i can use such type of pumps in my case.

i discussed this problem with the consultant and he refuse and said the pump shall be positive displacement type and i told him centrifugal pump can work.
pls. advice if it shall be positive displacement type or centrifugal pump type.

RE: very complicated installation case

It depends on the application which you have not told us about at all.

If correctly installed and fitted with a foot valve the split case pump you have should be able to work with a three meter suction lift but whether it is the correct pump for the application i cannot say based on the information provided.

For any of us to give an opinion you would need to provide the pump curve for the split case pump and the total head, anticipated flow and the application that the pump is being used for. You also need to tell us the type of liquid that is being pumped ,whether or not it has solids in the liquid the liquid temperature and the approximate altitude above sea level of the site.

Is there a reason that the consultant wanted a positive displacement pump?

Regards
Ashtree
"Any water can be made potable if you filter it through enough money"

RE: very complicated installation case

Why NFPA, is this a firepumps installation?

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)

RE: very complicated installation case

NFPA20 section 6.1.2 forbids use of centrifugal pumps where a suction lift is required.

Therefore " I need a reference from NFPA that I can use such type of pumps in my case." is not possible

This was apparently due to foot valve failures and vacuum lift failures.

A PD pump has no such limitations in NFPA 20.

If you want to use this tank at that level then you either seen a vertical turbine pump suspended into the tank or a PD pump.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: very complicated installation case

(OP)
thanks a ltot for your advice

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close