motor contactor sizing
Hi everybody
I want to get a good way to calculate the right size of contactor that is suitable for 3phase motor ; to be clear I want to know ;should I use the rated current or starting current ?
Thanks for all
Thanks for all
RE: motor contactor sizing
NEMA rated contactors are more conservative (hp-to-hp) than their IEC counterparts. There is nothing wrong with IEC contactors, just be aware they rated differently.
GG
David is correct: all motor contactors are rated in motor hp (or motor kW)
"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)
Bill
"Why not the best?"
Jimmy Carter
Just be aware that a motor which has a higher than typical FLA might need special consideration. When using NEMA rated contactors you generally can size HP to HP, but with IEC you have to pay more attention to the FLA of the motor. For example, a slow speed motor can have a much higher FLA than normal and require an oversized contactor.
Did you mean to say "LRA" (locked-rotor) and not "FLA" (full-load) above?
Curious,
GG
High pole-count motors have higher no-load current and full-load current than the more typical 4-pole motors. IEC motors are sized based on power output and the kW ratings printed on the contactors are based on the most common 2-pole and 4-pole motors, so if you have some oddity like an 8-pole or 12-pole machine then selecting the contactor based on the kW rating printed on the contactor will likely lead to an undersized contactor being chosen.
A similar argument probably could be applied to the LRA of certain motors though.
Got it. Thanx
GG
To put what my colleagues have said on non-country specific terms, contactors used for controlling motors must be selected based upon the listed and labeled motor POWER rating (be it HP or kW), not the current rating alone (with a nod to the outliers where the motor FLC is higher than normal)
. This is because there is more going on than simply the running current, and although not technically unacceptable, if you sized every contactor for the starting current, they would last forever but you may break your budget.When a contactor is rated for a particular induction motor power rating at your given voltage, it is inherent in the design that the contacts will handle the FLC continuously as well as any LRC that a motor of that size will be expected to draw under normal circumstances.
From that point is where IEC rules and NEMA rule diverge. IEC sizing rules include a specifically detailed duty cycle capability, with limits on the number of cycles per minute and minimum times between cycles before you begin a de-rating process, so the selection involves some minor engineering function to know how they are intended to be used. NEMA designs are intended to take the absolute worst case scenario and survive, after being selected by an electrician with little or no engineering background nor concern for how it might be abused.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
In general terms a NEMA contactor is pretty much equivalent to an IEC contactor sized according to its rating under AC-4 conditions (plugging / inching / jogging). IEC contactors are typically marketed based on the much less onerous AC-3 rating (DOL) and it usually works out that there's a full frame size difference between contactors sized for AC-3 and AC-4 duty. It won't come as a surprise that AC-4 contactors are pretty close in size and cost to NEMA contactors, while AC-3 contactors are considerably smaller and cheaper than a NEMA type.
Keith Cress
Thanks.
We have a lot of NEMA stuff where I work as a result of a joint venture between GE and the British company Allenwest in the 1970's which carried the 'Simplex' name. I think the deal was pretty much to produce GE's 7700 series MCC's under license in the UK. The NEMA gear has lasted very well, although at forty-odd years old it is starting to get tired and direct equivalent spares are harder to find without resorting to expensive imports from your side of the water. When we have to replace an old NEMA contactor I tend to use the AC-4 rating as the starting point for identifying an IEC replacement. The additional component cost is more than offset by improved reliability and longevity.
I can't think of any jobs I've done that needed plugging or inching type processes but I'll certainly keep that in mind now. Actually, most of the IEC stuff is so inexpensive I usually figure out the required and then go up another size anyway since $10 or $15 doesn't bother my customers. Heck, they're still surprised by the low cost since they all realize they'd be bent-over if they went down to the local electrical supply without a contractor's license and bought the wrong stuff themselves. :)
Keith Cress
I remember one 40 HP with only a start button and a jog reverse button. To stop you hit the jog reverse. If there was a jam-up that had to be cleared quickly the operator would hold down the button until the motor was stopped visually, then start jogging reverse until the jam-up cleared.
Don't try that with a T-frame motor unless you have spare motors in stock.
Some folk made a distinction between jogging and inching.
Jogging was repeated short starts.
In some usage inching was a primitive form of low frequency drive.
I have never seen such a drive but it was covered in some old text books. Inching may be used when a very large machine needed to be precisely positioned for maintenance.
A drum switch with continuous rotation controlled a bank of contactors, closing and opening them is sequence to produce a pseudo three phase source with a stepped wave form. A DC welding machine or similar supply may be used.
I mentioned this method here some years ago and was dissed.
Then one of our Gurus posted a short video of a bank of contactors being used in an inching application as I had described.
The motor rotation follows the rotation of the drum switch giving slow controlled rotation in either direction.
With a slower speed motor it was possible to position the machine to within less than one revolution of the motor.
Bill
"Why not the best?"
Jimmy Carter
Did the sift starter give the precision of the original system?
There was a similar video posted or linked on Eng-Tips some time ago.
Bill
"Why not the best?"
Jimmy Carter
You were right Bill, here is the link to where LionelHutz posted his video a couple of years ago. Good memory.
Can't make the video play any more however. Pity...
http://www.eng-tips.com/viewthread.cfm?qid=247294
Bill
"Why not the best?"
Jimmy Carter
Terrible video quality but you get the feel for this strange piece of equipment.
Is it worth the hassle to see the vid Scotty? What's it actually showing, just the ball mill or the contactors?
Keith Cress