Smart questions
Smart answers
Smart people
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login




Remember Me
Forgot Password?
Join Us!

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips now!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

Join Eng-Tips
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Donate Today!

Do you enjoy these
technical forums?
Donate Today! Click Here

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.
Jobs from Indeed

Link To This Forum!

Partner Button
Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum.
Just copy and paste the
code below into your site.

DiscoP (Electrical) (OP)
15 Jan 03 20:54
Hello All
A colleague of mine was recently testing a 415/110 V 3 limb VT. When injecting phase-phase on the 415 V side using a variac the secondary measurements were hopelessly out, but if a full three phase injection was performed with a test set then the secondary measurements were as you would expect.
The VT was totally isolated from the rest of the network.
3 limb VTs won't produce zero sequence voltage but there shouldnt be any zero sequence for a phase to phase injection.
Is there anyone here who might be able to offer an explanation. It is probably something obvious but none of us here can think of it !
raghun (Electrical)
16 Jan 03 5:00
DiscoP,

This is due to the diffrence in magnetic path reluctance values. To explain further, when you energise 415V/sqrt3 winding on the middle limb, the voltage induced in the 110V/sqrt3 winding on the middle limb will show expected voltage whereas the other two would show half the middle limb winding voltage (for a star / star VT). In case of extreme limbs, the induced voltage will be 2/3 in the adjacent limb and 1/3 in the far limb winding,approximately.
This phenomenon is familiar for the engineers involved in transformer testing and is called Magnetic balance test.

Raghunath

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close