When designing a high power high voltage resonant system for cable or motor and generator testing, or as a general question, when is a separate exciter transformer used in a parallel resonance circuit? They are always used in Series Resonant systems but not in Parallel Resonant systems. When and why the exciter in PR test systems?






RE: Resonance Test Sets for HV testing
RE: Resonance Test Sets for HV testing
Separate exciter transformers can provide additional functionality to the overall system in many applications. Due to the nature of a variable gap transformer, electrostatic shields used to decouple noise from the mains are not suitable (partial discharge testing). Also, any insulation failures between the LV and HV windings of the transformer are immediately coupled directly to the mains. As many of these systems are designed for mobile use and subjected to harsh environmental and testing scenarios, any protective measures designed to provide the maximum safety of all personnel and connected equipment is paramount. A properly designed separate exciter can provide significant additional safety levels.
A separate exciter provides the ability to "separate" the power ground from the high voltage test ground. Transient currents and voltages are present during any load failure (always expected) and the ability to control these transients and protect adjacent circuits is imperative.
Additionally, a separate exciter transformer allows for the ability to reconnect the system as a Series Resonant test system and realize all of the advantages this test circuit provides. Having an integrated "exciter winding" as a portion of the variable gap transformer "Parallel Resonant" test system precludes this flexibility.
RE: Resonance Test Sets for HV testing
I see you left your web address. I know your company and will contact you outside of this forum.
Thanks again.