We have a 460V, 60Hz, 1775RPM, 75HP motor connected to a positive displacement pump.
The VFD is ABB, I'm hoping there is an expert on these drives.
If the pump stops under load the discharge pressure is maintained by a check valve. On restart the motor is unable to pull away under pressure, I suspect this may be something to do with the current VFD setup.
No the motor and drive are at a remote site, I haven't been there.
Parameter 2101 set to 8 (Ramp) is that right for a constant torque load?
Are there any other parameters important for this sort of load?
Someone suggested We need an oversize VFD for this type of load.
Thanks in advance.
Roy
The VFD is ABB, I'm hoping there is an expert on these drives.
If the pump stops under load the discharge pressure is maintained by a check valve. On restart the motor is unable to pull away under pressure, I suspect this may be something to do with the current VFD setup.
No the motor and drive are at a remote site, I haven't been there.
Parameter 2101 set to 8 (Ramp) is that right for a constant torque load?
Are there any other parameters important for this sort of load?
Someone suggested We need an oversize VFD for this type of load.
Thanks in advance.
Roy





RE: ACS550 Parameters
So a VT rated drive will provide maybe 150% torque for a few seconds, 110% for 30 seconds, 100% continuous. But a CT rated drive will allow for 200% torque (maximum Breakdown Torque of the motor) for a few seconds, 150% for 1 minute, then 100% continuous (likely a little more). So if you bought your drive as VT because someone mistakenly said "Pump" and ASSumed centrifugal, you may have the wrong drive for the job.
If it is a CT rated drive, then what you likely need to do is to put it in Sensorless Vector Mode. In that drive, you would set 9904 to "Vector Mode". You will then also need to perform an "ID Run" for the drive to auto-tune itself to the motor (critical). That is done in 9910 by setting it to 1, but read the instructions on this for other tasks involved.
Once you do that, set 2101 back to 1 (Auto) for the best starting.
"You measure the size of the accomplishment by the obstacles you had to overcome to reach your goals" -- Booker T. Washington
RE: ACS550 Parameters
Sometimes these (PD) pumps will be equipped with a by-pass loop. Do you have one of these?
BTW what is the voltage at the motor (or VFD)? A lower voltage will impact the torque that a motor can develop (even on a VFD).
"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)
RE: ACS550 Parameters
The information you provided will give our mechanical engineer some good questions to ask.