can someone help me out how to check Single point ground on CT with multimeter or with megger?

RE: electrical

To prove the CT is earthed (grounded) at exactly one location? Lift the known earth connection and then megger the CT (or CT group) secondary winding to earth. If the reading is not very high then you another earth path. Reconnect the earth afterwards!

RE: electrical

Watch for hazardous voltages to build when you lift the ground if the CT's have current going through them during the test.

RE: electrical

buzzp brings up a good caution - but I would go one further and say do not try this with current going through the ct. CT circuits should not be disturbed while in service. Especially if you are not familiar with how to use simple test tools to perform this check. Open CT circuits are very hazardous and can start fires, damage/destroy equipment, or injure/kill you.

RE: electrical

Yes, completely agree. I'd assumed that this was a construction / commissioning activity without the circuit being energised, but very valid points.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources